The question,
A BS 88-3 fuse protects a 20A radial socket outlet circuit. The circuit is wired using 2.5mm single core cables installed in a 16m lenght of PVC conduit. A separate protective conductor consisting of a 1.0mm PVC cable is used. Assuming that no correction factors are applicable and that the value of Ze is given as 0.5 ohms, Determine weather the circuit complies with IET wiring Regulations for shock protection?, the norminal voltage (uo) may be taken as 23o volts.
My attempt at an answer.
Max Zs 2.04 ohms
Zs = Ze + ( R1+R2 x mf x L)
Zs = 0.5 = (25.51 x 0 x16)
1000
Zs = 0.5 + 0.4
Zs = 0.9 ohms
The circuit would comply with IET wiring Regs for shock protection because it is under 2.04 ohms.
Can anybody tell me if im the right track with the answer????????????
Thanks.
A BS 88-3 fuse protects a 20A radial socket outlet circuit. The circuit is wired using 2.5mm single core cables installed in a 16m lenght of PVC conduit. A separate protective conductor consisting of a 1.0mm PVC cable is used. Assuming that no correction factors are applicable and that the value of Ze is given as 0.5 ohms, Determine weather the circuit complies with IET wiring Regulations for shock protection?, the norminal voltage (uo) may be taken as 23o volts.