Odd one. Installed a system last Thursday. all tested. All good.
Went back to adjust panels and as soon as we reconnected the RCD tripped... and continued to (and stand-alone). Seemed to trip as we approached 2kw (of 3.8) but might have been coincidence.
Checked the IR for the cable run. Fine.
(BTW found 12v between the racking and scaffolding (not sure how) but found this in an identical combination around the corner and that's fine).
Any ideas what to look at? I guess even if there was a short on the adjusted panels (ie we damaged a cable or connection) it wouldn't show up on the AC side.
Confused and p*ssed off - it;s the first time with an Aurora inverter and I suspect it...