Discuss High reading on a R1 + R2 test on a ring main in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
S
Simon Hall
Hi I've done a ring main R1 and R2 test all my readings are around 0.15 ohms apart from one which is much higher at 0.83 it is not on a spur it is part of the ring any ideas or is this ok thanks
Try taking the reading inside the socket at the terminals before doing anything else. The last time I had this it was a duff socket. Otherwise, are you sure it is on the ring?
Cheers mate I give that a try, yeah it's defiantly on the ring as it's on a rewire I did only has 2 rings mains for power up and down
Where your r1, r2 & rn readings consistent?
Then your R1 + R2 reading should be around 0.07 - 0.08 ohms so IMO there is something amiss with your testing methods. Was the figure of 8 connected correctly?