I have bowed to the inevitable and issued the EICR with a code 2 for the high Zs. While I still do not agree I've no doubt the NIC will say a code 2 and that seems to be the majority view on here. Remedial will only involve changing a type C for a B, which will no doubt prompt comments about why bother making a fuss. Well I like coding to be correct and justified on my reports regardless of the cost of rectification.
 
I think you are taking the correct action in both cases, code 2 for the New World Order, and feeling that you do not agree but want to get things correct and justified.
The risk assessment would say
Hazard: long disconnection time
Likelihood: 0.0001%, low 1,
Effect: death, high 5.
Risk assessment overall 5, low risk, no action to take, no control measures required.
Overruled by IET random thoughts.
Full control measures to be implemented.
 
I'm not going to argue with anyone who advocates a code 2. That's an interpretation which can be justified. But my interpretation is that a compliant circuit is not safe one day and potentially dangerous the next simply because some boff playing with figures moves the goalposts to justify his existence.
However as already stated I will discuss the issue with my NICEIC inspector on his next visit and if he thinks a code 2 is appropriate then that's what I'll do in future...…(through gritted teeth mind you)

Why don’t you stick by your guns if you are so certain? What is it about your NICEIC Inspector that you respect so much?

If I was certain of ny stance I would be telling the NICEIC what I am doing not asking them if I can.
 
Mostly because inconsistencies in coding is an issue for recipients of EICR's. I think consensus and following established guidelines is important for an EICR to be credible, the worst EICR's I have seen are where the inspector has applied his own prejudices. I recall one where neutrals in a switch box had been given a code 2.
 
New posts

Reply to High Zs values (Just) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Hi everyone Recently I have come across an advert of someone selling Afdds C type and the person mentioned the need to sell because Zs was too...
Replies
16
Views
3K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
47
Views
8K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock