Hi all,

Only recently joined the forum, and thought i would get some views on the following.

Just wondered if anybody has had the following issues when fitting a new ccu.

Recently completed a rewire, including new new metal ccu, completed all dead tests ok, however upon live tests i got high zs readings on all circuits.

When i emailed the manufacturer`s technical support with my concerns i was told "most electricians in the know remove the rcd`s" or bypass them to conduct live tests.

I have never heard/had to remove an rcd for testing, in order to get lower zs readings.

zs =1.26
Ze= 0.22
Ring circuit r1/r2=0.38

Thanks
 
Probably from using low current no trip Zs. Try testing with the RCD's bypassed using high loop.

I have had trouble with RCD's on multiple occasions.

Edit - I only scanned your post but it seems the CU manufactures have advised the same.
 
Last edited:
Easy enough to prove actually. Carry out low current Zs at both sides of RCD and you can see what it is adding to your reading. I record this info on EIC that the RCD is adding X to cct Zs as it could take it over max Zs for OCPD even though it is the RCD that is adding it and ironically, the same RCD then additionally protects circuit upto a max Zs of 1667 ohms, so don't worry too much. I still record actual results though.
 
As others said, I would consider testing both sides of the RCD to ensure that's the problem, as long as the RCD is fine your result is still within the required maximum Zs. Nothing you can do about it really if it is the RCD, The R1 R2 is a reasonable figure.
 
Easy enough to prove actually. Carry out low current Zs at both sides of RCD and you can see what it is adding to your reading. I record this info on EIC that the RCD is adding X to cct Zs as it could take it over max Zs for OCPD even though it is the RCD that is adding it and ironically, the same RCD then additionally protects circuit upto a max Zs of 1667 ohms, so don't worry too much. I still record actual results though.

Are you saying that a RCD protected circuit doesn't need to comply with Max Zs for the associated MCB?
 
Its not ideal as its a bit of a get out of jail free card on TN systems for bad design Imo. But saying that it does comply...you are using the RCD for earth fault protection just like you would for a TT system with a high Ra. 50V is considered the safe touch voltage and you have a 30mA RCD so 50/0.03 equals 1667Ohms.
 
Last edited:

Reply to High ZS values on rewire in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
849
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
910
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock