''I had an interesting fault the other week whilst checking that Class 1 metal socket fronts were earthed. Admittedly it would have been best to carry out whilst dead, however this was just a quick check for peace of mind after doing a different job at night. I found 50v between the metallic light switch front and the main earth terminal at the consumer unit. When the light switch was switched on there was 100v. Further examination showed that the CPC (Earth) to the light switch was disconnected in the ceiling rose. Tests of the earth at the rose proved ok, IR tests on the switch cable proved ok. Reconnection of the CPC (earth) eliminated the problem. All I can put this down to is induction from the live conductors to the CPC conductor. One to look out for though''

originally posted by
topcop999

can anyone please explain why this happens?
Is it down to induction ?

thanks chris
 
bet he wouldn't have read the same with an AVO analogue meter!
 
Had a lady tell me that she kept getting electric shocks off her light switches. Her husband had told her it was just static.
I tested from main earth terminal to faceplate screws and read 230v
When the fuse board cover was opened up you could see that the shower cable had melted against the lighting circuit
 
Was the lighting cpc not connected at the board then? Should have been a big bang, not shocks from switch plates!

Or had that happened and blown the lighting cpc to smithereens and the shower fuse replaced?

Simon.
 
eons n eons ago as an apprentice i was screwing a switch plate back using a paint tin opener and it glowed we found the fauld was gompressed cable Joist had been cut to accomodate cables but cut wider than board leaving floorboards resting on cables and broken earth 6mm twe next to the 1.m we traced was squished so much it was same depth as 1.5mm but 4times as wide opened sheath and found the copper strands al spread out
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
how does a broken earth have volatge on it???
Prefix
N/A
Forum
Electrician Forum
Start date
Last reply date
Replies
5

Thread Tags

Advert

Thread statistics

Created
chrisreid186,
Last reply from
mogga,
Replies
5
Views
2,210

Advert