Just spent a frustrating day fault finding and still left scratching my head, was wondering if anyone else had experienced something similar!

The kitchen we had been working in had been a proper DIY job (diagonal cable chases, no earth sleeving etc etc etc) so we were testing a ring circuit to ensure it was indeed a ring before adding new sockets to it, when we found that the neutral and cpc had continuity between them. (0.16 ohms, e-e was 0.76 ohms, l-l 0.46 ohms) We then proceeded to remove all the other sockets, take up floor boards and check all the junction boxes, visually fine, yet neutral and cpc were still connected. We traced this all the way back to the fuse board (old re-wireables) where it became more interesting...

By switching off the main switch, the neutral-earth fault would be cleared on the sockets. Turn it back on, and the fault would come back. We then checked the cooker circuit, same problem...

Now, the earthing for the fuse board is not via an earth cable back to the incoming mains, it is clamped to a metal box which houses the meter, fuse board and incoming tails. There is another clamp that connect from the box to the incoming earth cable, such as in a TNS system.

I thought perhaps the incoming neutral cable had broken when being pulled through steel conduit between the fuse board and the meter, resulting in an insulation resistance fault between neutral and earth that way. replaced the cable, fault still there.

Worse still, even when the main neutral and main earth had been disconnected, i could still get a continuity reading between the earthing clamp on the incoming earth and the neutral bar in the fuse board. The result was over 600 ohms however.

This leads me to believe that somehow the incoming neutral cable is touching the steel wrapping of the incoming cable, under the ground somewhere? It must have been like this for many a year, and no fuse had tripped and no signs of damage, nicked cables, screws hitting cables when fitting the board/meter etc.

No idea how to proceed from here? Really stumped I don't mind saying! Has anyone had a similar experience or has any suggestions (other then run and hide!) that I could try?

I will try and get a photo of it all tomorrow if need be, I hope I have been able to give as much information as I can, if you need any more I will try my best to help!

Any advice appreciated, Joe
 
on TN systems, the earth and neutral are connected together. look at your diagrams of TN-S and TNC-S.
 
So you’ve ripped up someone floor to find a fault that isn’t there? N>E are linked at the DNO transformer no matter what system it is. Isolate both L & N before testing.
I hope you haven’t got the gall to charge the customer for this!
 
I might not have been clear in my description, but everything was disconnected, if you take out the incoming earth, live and neutral you shouldnt get continuity between earth and neutral bars in the fuse board?
 
bonding??? when IR teating a circuit, you should remove it's neutral fro the neutral bar.

testing. must have teats on the brain.
 
don't know about that. getting it caught in the L busbar might be painful.
 
Shame on you all, why have you all got to be so rude? Yeah okay i could have tested it better, i only qualified in june and first time ive been trying to sort this myself.

Sorry i wasted your time with this and my time for signing up. Seems to me like you'd all rather be coks then be civil.
 
Shame on you all, why have you all got to be so rude? Yeah okay i could have tested it better, i only qualified in june and first time ive been trying to sort this myself.

Sorry i wasted your time with this and my time for signing up. Seems to me like you'd all rather be coks then be civil.

Oh dear, dear, dear. Another newbie with very thin skin.

Apologies mate but you did yourself rather wide open with this one, and as you can see that others think this too.

And don't be rude to the people that tried to help you, all be it in a rather direct way else you will get kicked off.

Every day is a learning day
 
Don't worry about it, you just overlooked it and thought it might be more than what it was. No biggy, I forgot what ohms law was once. Back when I was 4 so it was ok ;-). It's done now, at least you bothered to make the effort in finding out why it was belling out, take it easy
 
The op's first post was in the new members bit , he has just deleted it and typed rubbish instead .
It originally said how he was a farther and son team and how his dad had been doing it for more years than could be remembered , I bet his old man just found this thread and tore him a new one for disgracing the family company in such away !:eek:mg_smile:

I wonder if they charged the poor sucker (who is now missing a kitchen floor) full rate for the lost day !?



Edit; Joe we all make daft mistakes mate , but it is the way we conduct our selfs after we realise the fact that make of the man !
 
The op's first post was in the new members bit , he has just deleted it and typed rubbish instead .
It originally said how he was a farther and son team and how his dad had been doing it for more years than could be remembered , I bet his old man just found this thread and tore him a new one for disgracing the family company in such away !:eek:mg_smile:

I wonder if they charged the poor sucker (who is now missing a kitchen floor) full rate for the lost day !?
Makes you wonder who taught him!
 

Reply to Incoming cable - earth neutral continuity! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
357
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
620
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
510
Been asked to do some rewiring, and have said needs upgrade of consumer unit really Main question is regarding earthing - Zs reads at 0.45 ohms...
Replies
7
Views
1K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
310

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock