Discuss Indicator switch with no neutral? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
138
Think i may be onto a loser here but is it possible to wire a simple one way switch and have some sort of indicator like a neon WITHOUT having a neutral? Its for the water pump to push hot water when required to kitchen tap (it's a long way from cylinder). There is already power at the pump, just need a switched live return.
I have a 3 core flex coming from the pump but the switch has to match the other fittings in kitchen and is metal fascia, hence needs a cpc! So my 3 wires are used up..
It may be possible to link a cpc from an adjacent skt but it's all newly plastered.. I know MK do a surround thing with a little led requiring no neutral but this is lit when OFF.
I assume neon grid modules need a neutral? I have a DP neon switch which was bought for it but obviously this needs a neutral.
Worst case is to just use an ordinary rocker switch with no indication but thought I'd ask.
Thanks..
 
Is there actually a UK reg forbidding this? I'd be interested to hear how it's worded.

The CPC is both functional and protective and often circuit elements in many appliances and light fittings such as noise suppressors, surge arrestors etc already use the CPC for their functionality. A neon indicator would be over a megaohm so the load current would be less than a quarter of a miliamp, this would be less than many suppression circuits might leak to earth.
 
Yes BS7671 states that a conductor identified as G/Y can only be used as a earthing conductor, not got the book to hand to state ref number though.

Functional conductors are identified as cream, although some RCBOs do come with a G/Y flying lead
 
What you could do is sense the flow of the alternating current of the motor when the pump is turned on by the switch instead of sensing the voltage applied to the motor. What you would need is a current transformer connected to a low voltage LED. A number of manufacturers make a ready made current transformer connected to an LED - all you would have to do is thread the load's line conductor through the current transformer's hole and drill a small hole in the switch plate to push the LED lamp through. If the magnetic field from one pass of the load line conductor through the CT is insufficient to light the LED then all you have to do is loop it though a second, third or fourth time - obviously there is a limit due to the CT's hole size and the diameter of the wire. The one I thought you might try is CR Magnetics CR2550-R:

http://www.crmagnetics.com/Assets/ProductPDFs/2550.pdf

which will light the LED at 0.75Amps AC for one pass through the 9mm hole. You could buy other colour LEDs.

They can be bought from:

CR Magnetics CR2550-R - https://octopart.com/cr2550-r-cr+magnetics-1186351
 
Yes BS7671 states that a conductor identified as G/Y can only be used as a earthing conductor, not got the book to hand to state ref number though.

Functional conductors are identified as cream, although some RCBOs do come with a G/Y flying lead
Change the colour from G/Y to cream.
 
The CPC is both functional and protective and often circuit elements in many appliances and light fittings such as noise suppressors, surge arrestors etc already use the CPC for their functionality. A neon indicator would be over a megaohm so the load current would be less than a quarter of a miliamp, this would be less than many suppression circuits might leak to earth.
Do you mean I cd wire a neon across s/L and cpc?
 
you could, but it's not recommended. marconi gave you the solution. in post #5
 
Can you not just pull a 4 core in with the old 3 core?
 
What you could do is sense the flow of the alternating current of the motor when the pump is turned on by the switch instead of sensing the voltage applied to the motor. What you would need is a current transformer connected to a low voltage LED. A number of manufacturers make a ready made current transformer connected to an LED - all you would have to do is thread the load's line conductor through the current transformer's hole and drill a small hole in the switch plate to push the LED lamp through. If the magnetic field from one pass of the load line conductor through the CT is insufficient to light the LED then all you have to do is loop it though a second, third or fourth time - obviously there is a limit due to the CT's hole size and the diameter of the wire. The one I thought you might try is CR Magnetics CR2550-R:

http://www.crmagnetics.com/Assets/ProductPDFs/2550.pdf

which will light the LED at 0.75Amps AC for one pass through the 9mm hole. You could buy other colour LEDs.

They can be bought from:

CR Magnetics CR2550-R - https://octopart.com/cr2550-r-cr+magnetics-1186351
That looks interesting Marconi, i shall try that. Many thanks..
 
Is there actually a UK reg forbidding this? I'd be interested to hear how it's worded.

The CPC is both functional and protective and often circuit elements in many appliances and light fittings such as noise suppressors, surge arrestors etc already use the CPC for their functionality. A neon indicator would be over a megaohm so the load current would be less than a quarter of a miliamp, this would be less than many suppression circuits might leak to earth.
I shall try that too, just to see! oh this is fun,...
 
Do you mean I cd wire a neon across s/L and cpc?
Yes, I was suggesting the neon between the switched live and the CPC. Electrically speaking I wouldn't really see a problem with such a small current flow and many appliances and electonic power supplies already regularly have components wired between the current carrying conductors of the supply and the CPC which introduce small leakage currents into the circuit..... I know it's not ideal and can even understand it being classed as bad prictice, the only thing I'm not sure about is whether the UK regs explicitly take it off the table as an option.
 
You can over sleeve green/yellow with another colour and use it differently in a multi core, except for a single cable.
The problem with t&e is the lack of insulation in the cpc. You would need insulation to mains voltage to use it for anything else.
Also even if the fitting doesn't need a cpc, you still need to provide one to every termination, so you'd still need one from somewhere.
 
Re used the cpc to power a very small load
, the only thing I'm not sure about is whether the UK regs explicitly take it off the table as an option.
Depends if you are using it as a combined neutral and earth, which is forbidden, or just for filtering.
I'd say technically the latter as you are connecting a load, but I'd not be overly concerned re the current.
 
I like Marconi's solution but wanted to add something about running a neon to earth. As per Marvo, there are filtering components in electronic devices connected from L to CPC, which are legitimate and necessary to combat radio interference. However they are required to meet certain constructional standards which you neon-with-current-limiting-resistor indicator lamp may not meet because it was not specced to run to earth.

If I had to do this, I would use a class Y capacitor as an additional current-limiting measure - these are permitted between L & CPC and also L and exposed metal of class II equipment, as they are self-healing and unlikely to fail short-circuit. FWIW If the indicator current is less than 0.25mA then even in the event of CPC failure, the current available to the touch is below the prescribed limit for class II equipment. But whatever is limiting the current must have proven durability and integrity, just like cable insulation.
 
What you could do is sense the flow of the alternating current of the motor when the pump is turned on by the switch instead of sensing the voltage applied to the motor. What you would need is a current transformer connected to a low voltage LED. A number of manufacturers make a ready made current transformer connected to an LED - all you would have to do is thread the load's line conductor through the current transformer's hole and drill a small hole in the switch plate to push the LED lamp through. If the magnetic field from one pass of the load line conductor through the CT is insufficient to light the LED then all you have to do is loop it though a second, third or fourth time - obviously there is a limit due to the CT's hole size and the diameter of the wire. The one I thought you might try is CR Magnetics CR2550-R:

http://www.crmagnetics.com/Assets/ProductPDFs/2550.pdf

which will light the LED at 0.75Amps AC for one pass through the 9mm hole. You could buy other colour LEDs.

They can be bought from:

CR Magnetics CR2550-R - https://octopart.com/cr2550-r-cr+magnetics-1186351


I have a similar situation whereby I need to light an indicator lamp when the outside lights are left on. Problem is, the outside lights comprise of 2 x 5w GU10's. I assume this means passing the wire through the hole around 18 times, is that correct, and doable with a 1mm cable?
 
I am just heading out the door but you are right that more turns will be required for the lower load current of your application. To light the LED requires 0.75 AmpTurns of alternating magnetic flux. As long as the product of load current multiplied by number of turns equals 0.75Aturns then the LED will illuminate.
 
[I said:
"Colin33, post: 1410887, member: 18528"]I have a similar situation whereby I need to light an indicator lamp when the outside lights are left on. Problem is, the outside lights comprise of 2 x 5w GU10's. I assume this means passing the wire through the hole around 18 times, is that correct, and doable with a 1mm cable?[/I]

The CT's hole is 9mm diameter. The diameter figure I turn up for solid single core insulated 1mm2 is in the range 2.1 to 2.5mm. I reckon this will pass through at most 12-13 times. So, you you will have to use a lower csa flex - say 0.5 mm2- and protect it with a 1 A fuse and mark up this maximum fuse size - see:

1 Amp Plug Fuse - BS1362 - https://www.tlc-direct.co.uk/Products/TLF1.html

http://www.batt.co.uk/upload/files/4f3a_1231500485.pdf

If it was me, I'd see if 12 turns of 1 mm2 provided sufficient LED illumination and if not then use the 0.5mm2 flex and 1A fuse method.

Sorry for the delay in answering this last part of your post.
 
Last edited:
The CT's hole is 9mm diameter. The diameter figure I turn up for solid single core insulated 1mm2 is in the range 2.1 to 2.5mm. I reckon this will pass through at most 12-13 times. So, you you will have to use a lower csa flex - say 0.5 mm2- and protect it with a 1 A fuse and mark up this maximum fuse size - see:

1 Amp Plug Fuse - BS1362 - https://www.tlc-direct.co.uk/Products/TLF1.html

http://www.batt.co.uk/upload/files/4f3a_1231500485.pdf

If it was me, I'd see if 12 turns of 1 mm2 provided sufficient LED illumination and if not then use the 0.5mm2 flex and 1A fuse method.

Sorry for the delay in answering this last part of your post.

Thanks, I'll give this a go. I was hoping to get this LED into the MK grid module ( Which I'd bought to do the job before realising the lack of neutral) but I think that may prove impossible. I'm wondering how neatly the led can be installed into part of the switch backplate, has anyone else done this before?
 
Colin33 - did you have a successful conclusion to this problem please?

(Sorry to nag because you are no doubt busy but the EF love to know the outcome of threads after advice is offered otherwise it is all theory - and we are practical people who want to know what works or not).
 
Colin33 - did you have a successful conclusion to this problem please?

(Sorry to nag because you are no doubt busy but the EF love to know the outcome of threads after advice is offered otherwise it is all theory - and we are practical people who want to know what works or not).
Hi marconi, the client has been away so I've only recently been able to discuss the options with him. He has decided to leave things as they are for now, and hopes that the new brighter LED lamps I've put in his outside lights will make it more obvious if/when they are inadvertently left on. I'm rather disappointed because I was looking forward to experimenting with the current sensor!
I thank you and everyone else for the valuable input :)
 
Using a CPC for anything other than it’s intended use is not allowed on BS7671, you could look at using a LED wired in series in your circuit.
Wrong - do people think that a piece of conductive material with green/yellow indicator sleeving works differently in any way than the other conductors?

It is a metal, the colour is only an indicator put there by the manufacturer for our convenience. If you then decide to place brown/blue/grey sleeving atop of the green/yellow, what possible difference does it make.

Earth core has not been bestowed with some magical curse, it is simple copper with a coloured cover. No decent Engineer would ever consider it any other way. The only consideration might be the reduced C.S.A. if it's PVC/PVC flat twin and skin.

In fact if you wanted to use g/y as line, blue as CPC and brown as neutral - with a good reason, there is nothing stopping you. The regs only state they should be clearly identified at access points and terminations. This could be the word LIVE, letter L, the word LINE, or a coloured section of sleeving.

AND... the regs are a guide, used to supplement/inform. We as qualified Engineers can deviate any way we choose, as long as it is safe, and justifiable.

Danny
 
Wrong - do people think that a piece of conductive material with green/yellow indicator sleeving works differently in any way than the other conductors?

It is a metal, the colour is only an indicator put there by the manufacturer for our convenience. If you then decide to place brown/blue/grey sleeving atop of the green/yellow, what possible difference does it make.

Earth core has not been bestowed with some magical curse, it is simple copper with a coloured cover. No decent Engineer would ever consider it any other way. The only consideration might be the reduced C.S.A. if it's PVC/PVC flat twin and skin.

In fact if you wanted to use g/y as line, blue as CPC and brown as neutral - with a good reason, there is nothing stopping you. The regs only state they should be clearly identified at access points and terminations. This could be the word LIVE, letter L, the word LINE, or a coloured section of sleeving.

AND... the regs are a guide, used to supplement/inform. We as qualified Engineers can deviate any way we choose, as long as it is safe, and justifiable.

Danny
Every cable must have a cpc in it.

Over sleeving the g/y to use it as a live conductor removes it as a cpc, and that cable no longer has one.
It doesn’t matter how short that cable is.
 
Wrong - do people think that a piece of conductive material with green/yellow indicator sleeving works differently in any way than the other conductors?

It is a metal, the colour is only an indicator put there by the manufacturer for our convenience. If you then decide to place brown/blue/grey sleeving atop of the green/yellow, what possible difference does it make.

Earth core has not been bestowed with some magical curse, it is simple copper with a coloured cover. No decent Engineer would ever consider it any other way. The only consideration might be the reduced C.S.A. if it's PVC/PVC flat twin and skin.

In fact if you wanted to use g/y as line, blue as CPC and brown as neutral - with a good reason, there is nothing stopping you. The regs only state they should be clearly identified at access points and terminations. This could be the word LIVE, letter L, the word LINE, or a coloured section of sleeving.

AND... the regs are a guide, used to supplement/inform. We as qualified Engineers can deviate any way we choose, as long as it is safe, and justifiable.

Danny

I think we're all well aware of the electrical properties of copper, regardless of the plastic covering it has. The issue is the identification, especially if the little bit of brown sleeving falls of at some point and someone assumes the grn/yellow wire is safe to touch.

The regs offer safe guidance in this case.
 
Every cable must have a cpc in it.

Over sleeving the g/y to use it as a live conductor removes it as a cpc, and that cable no longer has one.
It doesn’t matter how short that cable is.
Every final circuit must have a CPC, but it doesn't necessarily mean every cable has to.
 
Wrong - do people think that a piece of conductive material with green/yellow indicator sleeving works differently in any way than the other conductors?

It is a metal, the colour is only an indicator put there by the manufacturer for our convenience. If you then decide to place brown/blue/grey sleeving atop of the green/yellow, what possible difference does it make.

Earth core has not been bestowed with some magical curse, it is simple copper with a coloured cover. No decent Engineer would ever consider it any other way. The only consideration might be the reduced C.S.A. if it's PVC/PVC flat twin and skin.

In fact if you wanted to use g/y as line, blue as CPC and brown as neutral - with a good reason, there is nothing stopping you. The regs only state they should be clearly identified at access points and terminations. This could be the word LIVE, letter L, the word LINE, or a coloured section of sleeving.

AND... the regs are a guide, used to supplement/inform. We as qualified Engineers can deviate any way we choose, as long as it is safe, and justifiable.

Danny
Q1.53 Can a single-core cable having green-and-yellow insulation be used for any purpose other than a protective conductor?
No (with one specific exception). Single-core cables having green-and-yellow insulation must not be overmarked or otherwise identified, and must not be used for any purpose other than a protective conductor. The only exception is where such a cable is used as a PEN (combined protective and neutral) conductor, when blue markings must be provided at the terminations.
Regulation number(s):
  • 514.4.2
  • 514.4.3
 
Indeed it can, old thread but mk used to sell a neon indicator for light switches that connected across switch contacts. Haven't seen new ones for a long time but believe they are still available.
 

Reply to Indicator switch with no neutral? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Just a quick one, I want to use an ip rated light switch with a neon indicator to manually ovveride a PIR detector controlling an e27 LED...
Replies
1
Views
1K
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
366
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
484
Evening all, I had a quick Friday afternoon domestic job that has turned into a PITA and I'd appreciate your help. While adding some new lights...
Replies
10
Views
928
Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
715

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock