Discuss Infra Red radiators, or........ in the Central Heating Systems area at ElectriciansForums.net

How can you know what size CU your electrician will fit if you don't even know what heating method you will use and therefore the number of circuits required?

Why are you intent on installing ring circuits for the heating? This is a very poor installation design.

I expect he's already bought it!
 
I expect he's already bought it!
How can you know what size CU your electrician will fit if you don't even know what heating method you will use and therefore the number of circuits required?

Why are you intent on installing ring circuits for the heating? This is a very poor installation design.
The electric heating idea has only come along in the past month.
If I do go that way, why would it be a bad idea to have a separate ring? Such a load of 11kw, for several hours, on a circuit using other stuff too? Surely safer on its own ring?
Remember, there is no wiring at present, the previous wiring is ripped out, and it was all in the wrong place anyway. Nothing is chased out. The cables will be in conduit along the floor then hidden by the selotex/boards/laminate, upstairs the conduit will be chased out of the 70mm of screed on the concrete floor. I can have as many circuits as feasible, allowing for future expansion. The only extra cost is the pennies for cabling and the extra RCBO (Or whatever as necessary) in the CU. Sparky will be wanting 7-8k for the job, adding the odd £50 is nothing.
The price difference between a 11 way and 21 way CU is also lost in the noise.
 
Last edited by a moderator:
I'm not sure that electric heating technology is really racing forwards, resistive heating elements are as close as you'll get to a 100% efficient means of converting electrical energy into heat energy.

There are an awful lot of manufacturers claiming to have re-invented this particular wheel at the moment, I don't think any of them really have though!
Hence, as per my OP........I need real reports, not the "Frequently asked questions" of the websites selling the kit.
 
The electric heating idea has only come along in the past month.
If I do go that way, why would it be a bad idea to have a separate ring? Such a load of 11kw, for several hours, on a circuit using other stuff too? Surely safer on its own ring?
QUOTE]

A ring final circuit has been designed for socket outlets, not fixed appliances like your proposed heaters. It is not intend to connect such loads, and appendix 15 BS7671 recommends loads of over 2 kW, should have their own dedicated radial circuit.

A ring final circuit has been designed for socket outlets, not fixed appliances like your proposed heaters. It is not intend to connect such loads, and appendix 15 BS7671 recommends loads of over 2 kW, should have their own dedicated radial circuit
 
A ring final circuit has been designed for socket outlets, not fixed appliances like your proposed heaters. It is not intend to connect such loads, and appendix 15 BS7671 recommends loads of over 2 kW, should have their own dedicated radial circuit
It's good to know my logic thinking is in alignment with the law. Cheers.
 
The electric heating idea has only come along in the past month.
If I do go that way, why would it be a bad idea to have a separate ring? Such a load of 11kw, for several hours, on a circuit using other stuff too? Surely safer on its own ring?
Remember, there is no wiring at present, the previous wiring is ripped out, and it was all in the wrong place anyway. Nothing is chased out. The cables will be in conduit along the floor then hidden by the selotex/boards/laminate, upstairs the conduit will be chased out of the 70mm of screed on the concrete floor. I can have as many circuits as feasible, allowing for future expansion. The only extra cost is the pennies for cabling and the extra RCBO (Or whatever as necessary) in the CU. Sparky will be wanting 7-8k for the job, adding the odd £50 is nothing.
The price difference between a 11 way and 21 way CU is also lost in the noise.

A better design is to have a radial circuit for each heater, or each small logical group of heaters, e.g. Bedroom and associated ensuite on one circuit. The ring circuit was not designed for supplying fixed heavy long duration loads such as heaters, the advantages of a ring over radial circuit are lost when it supplies only fixed loads.
Individual circuits also result in much less disruption under fault conditions and can allow for simpler control wiring or more options for fixed overall control.
 
No it isn't, as pointed out in the post you quoted here the recommendation is for dedicated individual circuits, not a ring circuit.
Yes. Read it.
In the context of not having them on the main socket rings I mean.
Never even considered groups of radials though. I'll need to do some sums. Furthest room from CU will be 18 metres of cable and that was planned to have a 600w heater. Grouping that with the next room, which was planned 400w. Ideally next room also, with another 400w.
 
Yes. Read it.
In the context of not having them on the main socket rings I mean.
Never even considered groups of radials though. I'll need to do some sums. Furthest room from CU will be 18 metres of cable and that was planned to have a 600w heater. Grouping that with the next room, which was planned 400w. Ideally next room also, with another 400w.

Well that is why you pay an electrician to design and construct the installation!
That's a very precise cable length for a job that hasn't even started yet, are you certain of the cable routes that will be used?
 
Well that is why you pay an electrician to design and construct the installation!
That's a very precise cable length for a job that hasn't even started yet, are you certain of the cable routes that will be used?
I was going to do all the marking out and chasing out for the runs. So it's all measured. (I'm not now, sparky has better tools and will be faster). I had to plan the cable runs to avoid the plumbing runs for the wet system. But now the plumbing runs "May" not be needed. Although, I really need 1st hand reports from users of Far Infra red Rads., because although I'm sure that they feel fantastic when you are in direct line of sight of them, any obstruction will absorb the heat. So, for a ceiling mounted Rad, I will be toast up top, but my feet, under the table would be cold. That makes them c r a p. The blurb from the seller claims that the objects that are heated then warm the air. I'm not convinced on that. And how hot do the objects get, at 1 metre to 3 metres away?
Looks like I might have to wait for feedback from the user mentioned above. Unfortunately user is having them fitted in June so July would give a few weeks "Live" experience...............in summer, when they are not needed...... thus not really tested when somebody opens the front door for more than 3 seconds in December!
TBH, I wanted to embrace new technology, for its convenience and appearance, but it looks like I will be stuck with a biomass boiler the size of Africa in the Kitchen, and ugly fat wet rads. Possibly lose the downstairs rads to UFH, if I can sacrifice 1 inch off the 75mm insulation.
 
Hi guys. This issue hasn't gone away. I've moved off the Infra Red into modern convection.........I have done a nerdy level spreadsheet of Kwh usage for an electrically heated house. I reckon (3 bed semi, latest regulation insulated walls/ loft, concrete ceiling to downstairs) that the heating will be best case 11,000 kwh per year and worst case 15,000 kwh per year. The rest of the electric (From previous bills of a house where only the HW/CH was gas) are adding 6,800 kwh per year. At 15p per kwh this is giving me £236 - £282 range per month for electric.
The Bio Mass boiler option for CH and HW, plus the "Ordinary" electric works out at about £210 per month. So, it appears to be a no brainer.
But.
Biomas boiler including all Rads/Stores fitting is £14,000. The Boiler is about £5,000 which will beed replacing after 10 years, even though I've assumed £250 per year maintenance.
Electric rads purchase and 2 thermal stores and fitting (At same time as the house is wired (It has zero wiring now) is £4,600.
CGI grant available on Biomass, equates to about £5,000 over 7 years. This grant has already been cut back twice....I'm not holding my breath that it will stay good 7 years with *any* government scheme. However, the extra £9,000 of the biomass is borrowing on a mortgage. I don't need to use mortgage if it was all electric.
No gurt big boiler in my kitchen. No wet rads and plumbing. No flu.

Over a 10 year plan, the differences are lost in the noise in my opinion. But everybody says Electric heating is crap. I'm not seeing this....what am I doing wrong?
See summary spreadsheet file attached.
To remind you Gas is 100% impossible, Oil is possible but I need to bury / bund the tank in garden. Outlay was more than the bio mass.
Air pumped UFCH is possible, but one of *her* family has it, and they are sorry it was done, and wifey agrees having been there.

Heat.PNG
 
Hi - I thought an oil fired boiler, bunded tank, rads and pipes etc would be substantially less capital than £14k you've been quoted for biomass ?
 
Hi - I thought an oil fired boiler, bunded tank, rads and pipes etc would be substantially less capital than £14k you've been quoted for biomass ?
Quoted for a 2500 litre tank, 100% buried (Apart from that butt-ugly mushroom), bunded, encased in concrete etc. 12 rads, boiler, 2 thermal stores in loft....was £16k. Not much more, but more. Boiler was the ugly outside style though, I think they are more expensive than internal types due to waterproofing. Dunno, we've dismissed oil due to all the fecking about with it. And, as most of the nation needs electric, the prices will stay "Balanced". Whereas oil will increase more. Pellets will probably increase too, because why should market forces give a flying feck for a few thousand homes with pellets/oil. If you see my drift.
 
Burying an oil tank is a costly undertaking to be sure, but you can cut a lot off this if you are prepared to have the tank above ground as they are typically £1500 or so. Did they break down their quote at all?
 
Impossible above ground. Listed Grade 1 next door. All land covered by relating covenants.
The quote was not one outfit. Misleading in my narrative. I got 4 quotes for tank and delivery, groundworks and bunding, plumbing, and the two certificates of safety.
Plus, we dismissed it anyway. The garden is actually small, gurt big mushroom in it (Nah) and the vent plume from boiler will be near our seating area, both garden and bedroom verandah.
 

Reply to Infra Red radiators, or........ in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
214
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
1K
At the moment it depends on the weather on how well the central heating works, the main problem is the Nest Gen 3 thermostat only measures the...
Replies
7
Views
725
Hello. I’ve been racking my brain all day with this. Here is my situation and question: I have some OEM ambient lights in my vehicle. They are...
Replies
7
Views
993
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock