Job in a old shop, new board put in about 10 years ago, every test is fine but when we come to do the Live/Earth insulation test we get a low reading of 0.6M, now it's the same when turn off all the circuits! have dissconnected the neutral and nothing, tested from the live side of the switch to earth and THATS fine but when we try and do every circuit individually it's 0.6M (on or off) really stuck with this one!
any ideas would be great
sounds like a trapped cable in an accessory.
do each circuit separately and find the offending circuit that way then check accessories on that circuit.
done every circuit separately and the same, this is the second time this has happened too me on a job, first it was in a garage workshop, this one was in a shop!
got me fuxed
Did you disconnect the neutrals as well, I had problems before,but not with every circuit thou, but a group of circuits and found some circuits had a neutral to CPC fault and anothers phase to neutral and by not disconnecting netral keep getting Phase to CPC faults. Fault was long screw in cable not installed correctly, circuit were functioning no breaker where tripped, found two the screws to be live.
Reply to Insulation L/E Problems in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Insulation test live to earth = 0.7 ohms. This is a long length of buried swa cable (approx 100m) from mains in to submain. Test done with live...
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...