Job in a old shop, new board put in about 10 years ago, every test is fine but when we come to do the Live/Earth insulation test we get a low reading of 0.6M, now it's the same when turn off all the circuits! have dissconnected the neutral and nothing, tested from the live side of the switch to earth and THATS fine but when we try and do every circuit individually it's 0.6M (on or off) really stuck with this one!

any ideas would be great
 
sounds like a trapped cable in an accessory.

do each circuit separately and find the offending circuit that way then check accessories on that circuit.
 
sounds like a trapped cable in an accessory.

?

done every circuit separately and the same, this is the second time this has happened too me on a job, first it was in a garage workshop, this one was in a shop!

got me fuxed
 
Did you disconnect the neutrals as well, I had problems before,but not with every circuit thou, but a group of circuits and found some circuits had a neutral to CPC fault and anothers phase to neutral and by not disconnecting netral keep getting Phase to CPC faults. Fault was long screw in cable not installed correctly, circuit were functioning no breaker where tripped, found two the screws to be live.
 

Reply to Insulation L/E Problems in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Insulation test live to earth = 0.7 ohms. This is a long length of buried swa cable (approx 100m) from mains in to submain. Test done with live...
Replies
35
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
895
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
631
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
701
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
764

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock