Any feedback on this would be handy.

If you have a property that has a lot of lamps etc.. that are too much to remove to carry out a insulation resistance test why does it work that connecting the line and neutral together and testing between the two and earth.

Can someone explain.
 
With the lamps in , or anything else connected if you apply voltage to both lives you're energising both sides and then testing the IR to earth. You're testing the whole "business" side of the installation against the safety side. If it passes the test then there are no earth faults, so anyother fault should show as an overload or short circuit which if it is a working installation with no history of faults can be assumed to be free from faults? I think that's the right answer it makes sense in my head, but I'll happily be corrected!!
 
i think also, when you ir test the live and neutral you would get a dead short ie 0.00 because the bulbs connect the L and N and you end up with a loop back to your tester, depends how you ir test, i generally test, L-E N-E and L-N when doing the ir tests. hope that helps
 
As said you will get false readings through the lamps. Also to avoid damaging the lamps and any other sensitive electronic equipment by sending 500V DC between L&N.
 
As others have said there are 2 issues

1) to avoid false readings with line to neutral load in circuit
2) it avoids damage to sensitive equipment as in theory there is no circuit for the test current to pass through

I say in theory above because if there is a neutral - earth fault a circuit could still be completed which is why I test neutral to earth first when vulnerable equipment is at risk
 

Reply to Insulation Resistance Test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
706
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
During an insulation resistance test IR at an EICR I measured 0.0014 MegOhms from line to earth. When I disconnected the neutral from the neutral...
Replies
4
Views
1K
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
773
I am wiring up a new kitchen and conservatory. I'm not sure why I checked continuity between line and the metal back box of the light switch, but...
Replies
3
Views
760

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock