Insulation resistance testing hasbeen carried out on a installation in a shower block and the followingresults obtained
live to live = 200m ohms
live to earth = 0.5m ohms
a. are these testresults are acceptable:
b. The actions to be taken should thetest results be unacceptable are:
Anything above 1mohm is acceptable, although I personally would like to see more than that.
Providing you have disconnected all sensitive equipment, then you have an issue with the insulation breaking down between live and earth. The section of cable at fault will need to be replaced.
Has as been said the result look poor live earth have you checked for neons if their is one then it will need to be isolatted so have a good look round see if their is one the retest with it isolatted
yes. because you are leaving a load with a finite resistance across L and N.
Yes but a neon would not be across line and earth, unless its been installed by a cowboy.
Not sure of the effect of a neon, as IR tests are done with DC........
In any case, Paul.
This is obviously a college exam question, so you should be able to come up with an answer first. We could then give you some guidance. You'll not learn by just asking without making any effort.
*CLUE*
Have a look in BS7671 in teh section on IR testing and what the acceptable IR limits are. then you could come up with an informed answer.
so basically the actions the need to be taking is they needs investigating to find what is causing the results to be low. which something such as neons not disconnected before test. if we find what we think is causing it we need to disconnect it and do the test again until we get the reading over 1 mega ohms
Yes poor cable instulation damaged cable poor connections at switch or in the shower unit if its a electric type damp cable. loads of stuff but would need investigation as has been said are you new to testing it can take some getting your head a round hope I have helped.
SPD s can cause low line earth IR results and if they are class three can then be damaged by a 500V test since class three operate at 400V.
Make sure all sensitive equipment is removed from circuit before testing and (not according to the regs) test at 250v first, if you get a low result check the attached items again.
Neons tend to produce an IR value of about 0.1Mohms or 0.5Mohms Line to Neutral depending on type.
My most recent fault finding turned out to be a failed Fused Connection Unit.
Went down the route of "divide and conquer" found the area causing concern, disconnected terminations and results were great??? Connected accessories and tested again and fault was back. Removed accessories and tested between terminals of Fused Connection Unit and sure enough the fault was there. Replaced with new unit, retested continuity and IR and problem solved. :thumbsup
Reply to insulation resistane testing please help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...