In terms of testing the cabling there are two separate tests that need doing :

1) Check that (with all the heads removed) there is no connection between any of the four wires (including earth). If (say) the interconnect was shorted to the neutral then the interconnect wouldn't work and you'll get the symptoms described (only the one unit will sound).

2) Check that there's a complete link along each - i.e. L, N, and interconnect is connected between all the bases. As already said, if there's a break in the interconnect then the units will work in separate groups - those one side of the break, and separately the ones the other side of the break.

And for this size on installation, there really should be a test/isolate switch which for a hardwires system would be the one littlespark posted a photo of in post #76.
 
As an observation rental properties should not have battery backed ionisation alarms fitted , should be optical with built in rechargable battery ie:3016 from AICO , this applies in hallways and general living spaces , heat alarm in the kitchen , ionisation are acceptable in bedrooms.
 
As an observation rental properties should not have battery backed ionisation alarms fitted , should be optical with built in rechargable battery ie:3016 from AICO , this applies in hallways and general living spaces , heat alarm in the kitchen , ionisation are acceptable in bedrooms.
Where does it state this? I was advised by the local authority to fit a mains powered interconnected system. There was no additional stipulation.
Can you clarify please.
 
Wouldn't surprise me if he's also right on the requirement for mains +rechargeable

That's the way it should be for rented accommodation, as near as possible to a maintenance free system

So what the council are now requiring here(Eire) when leasing property for rental is a fire panel fitted , seems like overkill but...
 
This is from the Aico electrical contractors handbook
 

Attachments

  • 426DBB5C-4E82-492B-B936-80AE8C998208.jpeg
    389.9 KB · Views: 12
  • 1E38561F-40F4-45ED-9CB3-25F762B3C996.jpeg
    374.7 KB · Views: 11
So "recommended", not "mandatory". But I'd not user user-replacable batteries anyhow - to tenants they are either a nuisance that can be silenced by removing the battery, or a handy spare battery for something else ?
 

Reply to Interconnected smoke alarm - troubleshooting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I currently have a home with 7 interconnected, hard-wired smoke detectors. I have a hard-wired heat alarm in the garage that I need to have...
Replies
4
Views
2K
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
348
i had a builder do some work but now my smoke alarms turn off when the lights are off, does this mean i can only have a fire when the lights are on?
Replies
9
Views
862
Hi all! This weekend we have an offer on 8 of our most popular Smoke, Heat & CO alarms from trusted brands! Don't wait too long as these offers...
Replies
0
Views
384
Does anyone know what the new rules for England are for the rented sector smoke alarms and carbon monoxide detectors? Can they be battery powered...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock