I think the Aico call points look like 3 switches??. Like a remote test button?. Never wired one, so i dont know.




quick google: Is this it?
aico-ei1529rc-hard-wired-alarm-control-system-switch.jpg
 
That isn't a call point it is just a controller to hush and test them.
 
In terms of testing the cabling there are two separate tests that need doing :

1) Check that (with all the heads removed) there is no connection between any of the four wires (including earth). If (say) the interconnect was shorted to the neutral then the interconnect wouldn't work and you'll get the symptoms described (only the one unit will sound).

2) Check that there's a complete link along each - i.e. L, N, and interconnect is connected between all the bases. As already said, if there's a break in the interconnect then the units will work in separate groups - those one side of the break, and separately the ones the other side of the break.

And for this size on installation, there really should be a test/isolate switch which for a hardwires system would be the one littlespark posted a photo of in post #76.
 
As an observation rental properties should not have battery backed ionisation alarms fitted , should be optical with built in rechargable battery ie:3016 from AICO , this applies in hallways and general living spaces , heat alarm in the kitchen , ionisation are acceptable in bedrooms.
 
As an observation rental properties should not have battery backed ionisation alarms fitted , should be optical with built in rechargable battery ie:3016 from AICO , this applies in hallways and general living spaces , heat alarm in the kitchen , ionisation are acceptable in bedrooms.
Where does it state this? I was advised by the local authority to fit a mains powered interconnected system. There was no additional stipulation.
Can you clarify please.
 
Wouldn't surprise me if he's also right on the requirement for mains +rechargeable

That's the way it should be for rented accommodation, as near as possible to a maintenance free system

So what the council are now requiring here(Eire) when leasing property for rental is a fire panel fitted , seems like overkill but...
 
This is from the Aico electrical contractors handbook
 

Attachments

  • 426DBB5C-4E82-492B-B936-80AE8C998208.jpeg
    426DBB5C-4E82-492B-B936-80AE8C998208.jpeg
    389.9 KB · Views: 52
  • 1E38561F-40F4-45ED-9CB3-25F762B3C996.jpeg
    1E38561F-40F4-45ED-9CB3-25F762B3C996.jpeg
    374.7 KB · Views: 56
So "recommended", not "mandatory". But I'd not user user-replacable batteries anyhow - to tenants they are either a nuisance that can be silenced by removing the battery, or a handy spare battery for something else ?
 