Some advice please .
when doing IR test , generally i test the lighting circuit with the load shorted (L-N) and test across earth and live or neutral as removing all lamps and disconnecting fluorscents is time consuming .
now and again i will test the whole CU in this way .

Firstly , why is it that on some occasions a perfect reading (on a megger <999) is obtained , while sometimes anything between 10-800 Mohms is found .

secondly , when recording these results on the report is it correct to include the L-N column or not ?

lastly , how is it possible that when doing IR test normally (load not shorted ) a lower reading is sometimes found on N-E even though this is dead test and main switch is isolated

cheers
 
firstly. damp, dirt, dead spiders, etc.
secondly, if you don't measure L-N, then on the test sheet you should enter N/V.
for the last bit... parallel paths? bonding?
 
he's not. he means > 999 Ω , which is the megger's upper reading limit.
 
my mistake. was thinking of my megger BM401. that reads >999 on 500V test. the 1553 , as you say, is >299 on 500V.
 
Last edited:
Hello Jon,

I think the first question has been answered.. here is a link that gives a thorough explanation View attachment insulation resistance explained.pdf

As for the second question I was concerned about not filling in the L-N IR column but from other threads it seems this does not always get filled in (and like Mr DS said enter a N/V). However if I found any unsatisfactory L/N - E IR results on a circuit I would then do a L-N also just to do a thorough check.

I think the third question means why can N-E be lower than L/N-E with regards IR testing. I suppose if the Insulation on the L was pretty poor then the results would be better with a N-E test. But if you haven't unplugged everything or left the lights in then I would have thought they would be the same!
 
Last edited:

Reply to IR test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
582
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
387
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
632
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
734
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
627

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock