No, I opened up a new window just to wind you up!o ffs... did you deliberately leave those two tabs showing? You dirty old man
Thanks for your replycooker should not pull more than 32A
cable if it is H07RN-F as below is good for 35A
however as said before, it will not draw 32A in use for long, even if you have everything turned on.
Nothing to worry about.
View attachment 116029
Thanks for replyingas mentioned previously, you need to allow for diversity, you will not pull enough load to worry the 4mm2 cable you have