Search the forum,

Discuss just failed eicr in the UK Electrical Forum area at ElectriciansForums.net

regarding cpc i re connected as soon as i noticed .

basically this guys needs these circuits rewired that failed IR
flat is around 25-30 year old
but the fact that the shower is wired in 2.5mm through a sw/fuse spur from day 1 is SHOCKING , (theres no bath only shower)
heard from maintenance plumber that all the flats are F***** lol

What type of shower is it?
 
Landlords are the worst for getting things done, and they should be the ones who should want to get it sorted. If i was a landlord id sleep better at night knowing my property and tenants are safe, IMO :)
 
DIY disaster been going on there,today i went to a cafe where the new owner had decided to wire up his own 3 phase fryers x 2 and a fish fryer on 1 single 15A 3p supply with an adaptable box it had 6mm singles in and 3 x 1.5mm coing out then into commandos,the bloke said he wondered why there was a smell of burning,crikey,diy home improvements are one thing but now they want to diy the light commercial stuff too.What next!!!
 
DIY disaster been going on there,today i went to a cafe where the new owner had decided to wire up his own 3 phase fryers x 2 and a fish fryer on 1 single 15A 3p supply with an adaptable box it had 6mm singles in and 3 x 1.5mm coing out then into commandos,the bloke said he wondered why there was a smell of burning,crikey,diy home improvements are one thing but now they want to diy the light commercial stuff too.What next!!!

the worst lol

what you think of my test results , i done it 3 times as i didnt want to take them for granted incase i left things plugged in etc ,
linked lives and tested to earth
 
0.00
0.00
0.46
0.34
0.00

Without meaning to sound like I'm taking a pop at you, which I'm not as I don't know you, are you confident that you are testing correctly? As with those figures something is seriously amiss somewhere.
 
Without meaning to sound like I'm taking a pop at you, which I'm not as I don't know you, are you confident that you are testing correctly? As with those figures something is seriously amiss somewhere.

lol i actually second and third guessed myself mate, cooker circuit >999Mohms

the rest tested same way (correct way) they all failed

- - - Updated - - -

Looks like equiptment still connected or neons L-N,not questioning your expertise,i didnt read earlier posts were any of these circuits still in use?

tested lives-earth for these readings
 

Reply to just failed eicr in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, recently had an EICR test done by 'Landlord Certificates' which failed due to circuite 3 having two radial circuits into a single 32amp MCB...
Replies
31
Views
4K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
784
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
962
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
899
Went to fix a simple issue for someone . Then realised they where tenants and asked if they had a copy of the EICR ....NOPE . Turns out no Gas...
Replies
1
Views
725

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top