Hi all,
if using 2.5mm can i put a 16A MCB on a lighting circuit? never needed to before so a little unsure, but can't remember of they're limited to a certain amperage.
thanks
Depends on the fittings , if fittings are only wired in small guage wire then you can't.. also what are the switches rated at..
I would say that if designed correctly (i.e 1 fitting at a time tapping off the 2.5), then smaller condutor size for the fitting is fine. You could design it to omit overload current. Im thinking of lighting support couplers specifically.
If you're on about going to an existing installation and just want to uprate the MCB, then you'd need to make sure the circuit is suitable to do so.
My Thoughts are that the internal wiring within many fittings you find are quite small, with many fittings that can be connected to a circuit like this such as modular fittings have in line fuses within the fitting , I was thinking more on the lines of domestic fittings.
not series though are they...
To be honest i would ask my self why 16 amps that's an awful lot of lights i would look at splitting the circuits to reduce the loads rather than increase the cable and MCB size , also depending on the lights you may require a C type breaker if the lights are discharge etc
If you feel you need to, fit a spur at each light and fuse it down for the final flex.
Often done for substantial wall mounted externals.
Call it a maintenance switch.
Boydy
If you have BC or ES lampholders you are limited to a 16A OCPD, if not then it is down to the fittings.
look its the same old story Richard...attempting to combat inrush by going for a higher I N...rather than doing the correct thing which is assessing the characteristics of this circuit & connected loads...then choosing the correct OPD to suit...
Reply to Lighting circuit MCB size in the UK Electrical Forum area at ElectriciansForums.net
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Hi all. Removed an ancient light fitting, replaced with a newer one, the light comes on but can't be turned off with the switch. It was working...