Yep, 100% it is on a 15amp fuse, earthing of lighting circuit is satisfactory, but am unsure why I need to upgrade bonding???
You don’t necessarily need to upgrade any protective bonding conductors , just need to verify they exist if required and are satisfactory.
If extraneous conductive parts exist within the installation and do not have any protective bonding conductors Connected to the MET then your work can not proceed.
 
To be fair there are regs in place for additions to existing circuits , if no rcd is in place the supplementary bonding can not be excluded.
 
A lighting circuit on a 15a fuse would ring alarm bells for me. Particularly as from the questions the OP is asking I doubt he has the competence to verify a safe addition to an existing circuit.
 
Can you not spur from the ring/radial circuit and put it on the other side of the wall of the bathroom? But 15a lighting circuit, never seen it, must get out more.
 
Only time I see 15amp lighting circuits are older commercial properties/factory units where the lights have been wired in pyro 1.5mm or 2.5mm for banks of fluorescent lighting.
Even then they are bs 3871 devices so 16amp.
 
Thinking vorti is being practical here. Even if dropping circuit into bathroom, feed it out to hall/bedroom and keep CU out of the bathroom, leaving you options for cabling under floor/bath/whatever?
I say this not as an expert, but I know my spa bath has a power supply from the loft, via an RCD in the bedroom cupboard, to a switched outlet and then through the bedroom wall, under the units to the bath motor, thus no connections in the bathroom at all, apart from the final ones at the motor...and the same for the electric shower. I bow my head to those who really know about these things, naturally...
 

Reply to Macerator spur from lighting circuit??? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Just interested in peoples thinking on using the neutral through the earthing system like I came across today. I've come across many wrong...
Replies
10
Views
2K
Hi all, I’ve recently had my boiler moved from the kitchen to the airing cupboard upstairs. (Changed to combi) Prior to this the hot water tank...
Replies
11
Views
2K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock