Hi all,

I’ve recently had my boiler moved from the kitchen to the airing cupboard upstairs. (Changed to combi)

Prior to this the hot water tank was in the airing cupboard which was being powered from its own circuit on the consumer unit. There was a shower pump powered from an FCU running from the hot water tank circuit.

The current boiler is run off the same circuit on a 3A FCU. The actual circuit is only powering the FCU at the moment.

If I wanted to put an LED batten light in the loft which is directly above, could I run the light from the boiler FCU? So the LED light and boiler are on the same FCU.

The loft is fully boarded so don’t want to cut into it to get to the light circuits.

Many thanks,
J
 
Last edited by a moderator:
Personally I wouldn't put them on the same FCU... if the light goes bang, you could be left without heating/hot water. I would install a second SFCU to supply the light on it's own 3A supply.
 
Electrically no problem, but i like to have important stuff like heating on its own circuit.
 
It would also require 30ma rcd protection.
 
  • Like
Reactions: DPG and SparkyChick
Thanks for the replies. Yeah I did consider that. So I can just run another FCU from the current one with a 3amp fuse?

Alternative, if I need to lift the boards, I take it I can just cut in to the existing light wiring supply feed and chuck a wago box with connectors on it and do it that way?
 
Thanks for the replies. Yeah I did consider that. So I can just run another FCU from the current one with a 3amp fuse?

Alternative, if I need to lift the boards, I take it I can just cut in to the existing light wiring supply feed and chuck a wago box with connectors on it and do it that way?
I would suggest if you are going to your latter suggestion you seek the services of an electrician and not suggest solutions you have found on the internet, it also requires 30ma rcd protection.
 
  • Like
Reactions: nicebutdim
I would suggest if you are going to your latter suggestion you seek the services of an electrician and not suggest solutions you have found on the internet, it also requires 30ma rcd protection.
Thanks for your reply, which wasn’t really helpful and how have you come to the conclusion that the solutions have been found on the internet. Isn’t the point of this forum to ask for advice, which if you read back, that is what I have done. Thank you.
 
Thanks for your reply, which wasn’t really helpful and how have you come to the conclusion that the solutions have been found on the internet. Isn’t the point of this forum to ask for advice, which if you read back, that is what I have done. Thank you.
Whilst the forum is happy to give DIY members advice a line must be drawn if you are suggesting solutions which are beyond your level of competence, yes I know it's just wires. As for internet where have you found the term Wago box.
 
Whilst the forum is happy to give DIY members advice a line must be drawn if you are suggesting solutions which are beyond your level of competence, yes I know it's just wires. As for internet where have you found the term Wago box.
To play devil's advocate - is wago'ing from an existing lighting circuit really beyond...well anyone's competence?
 
  • Optimistic
  • Like
Reactions: UNG and Jay92191
To play devil's advocate - is wago'ing from an existing lighting circuit really beyond...well anyone's competence?
Wago is a brand name and not a type of connection. Is it beyond anyone's competence well, it is beyond some and within others. Does this circuit have 30ma rcd protection.
 
To play devil's advocate - is wago'ing from an existing lighting circuit really beyond...well anyone's competence?
It's not just about doing the work itself... it's about the additional testing we would do (with equipment no home owner or DIYer is likely to have or want to shell out for) to ensure that the works have not compromised the safety of the circuit.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Loft light from Boiler FCU
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
Jay92191,
Last reply from
brianmoooore,
Replies
11
Views
2,749

Advert