Discuss Main bonding lead water pipe? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
G
gesl
I have a CU change job and the water pipe supplying the house is lead. The lead enters the house then runs right under the house and into the kitchen where it is jointed to copper. The regs say bond where it enters the house (which is convieniently underneath the CU), but there appears to be some argument wether it is ok- and how- to bond to lead pipe.
What is right? and where is it in the regs?
Assuming you were using it for your competent persons inspection and had to explain your reasons, what would you do?
Cheers
GESL
Cheers
GESL
There is a big difference between a lead water pipe and a lead gas pipe-the water pipe is designed to cope with a much higher pressure and uses a strengthened wall making it suitable for a conventional BS951 clamp.
There is a constant pressure spring clamp available too if you'd prefer to fit that.
I don't know what you mean by 'some argument' if the pipe enters the property near the consumer unit then you bond it within 600mm of that point with the usual proviso on joints/branches.
Teletrix, thanks for the reply. There is a stop cock in the road about 1 meter from where the lead pipe enters the house under the floor in the living room. There is a small amount of exposed pipe in the living room. Then where the pipe comes out the floor in the kitchen there is a valve where the join is to the copper pipe.
Cheers
join it at the most accessible and easiest point you can achieve. (preferably copper) but as IQ said the Lead will be able to withstand bit more pressure than gas pipes!!
Thanks for the reply IQ. I have read in lots of places, including manufactures info that some BS951 clamps are not suitable for lead. Depending on who you ask you get a different opinion. I have searched high and low for the spring type clamp but can't find them anywhere, details would be appreciated.
The 'argument' I talk of is basically the difference in peoples opinions/interpretations of the regs.
Cheers
go with IQ's post. as he says lead water pipe is much thicker walled than lead gas pipe. it will stand a bog standard BS951 clamp without a problem.
been trying to get hold of them for ages. local wholesalers ain't got a clue what i'm on about.
A clamp on the lead it is then! Thanks for the info on the constant force spring clamps, I think I'll try one of those.
Cheers for all your thoughts
A standard BS951 will be fine for a pipe, but clean the lead with emery or the flat of a knife blade first. The wall of a lead water pipe is over twice as thick as the lead sheath on a cable.
I’ve worked on lead cables, gas pipes and water pipes. Not just putting clamps around them but joining them.
Lead isn’t as delicate as people think. The first time I was given a lead sleeve to beat for an 11KV joint I was tapping at it while the guy teaching me was howling with laughter, within a few minutes I was quite happily belting away at it. Just wish I’d still got my lead beating tools.
Reply to Main bonding lead water pipe? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...