Piratepete

Hi Guys
I'm working in a house which has 2 consumer units. One supplying the original house is by the DNO's cutout and meter through Henley blocks. Installation is TN-C-S.
The other is some way away and supplies an extension. It is fed with a 10 sqmm T &E from a 45 amp DP switch fuse by and connected to the same Henley blocks.
IMO the 4 sqmm earth in the T&E is inadequate and it should be 10 sqmm.

Assuming I'm correct, it will be a challenge to route a 10 sqmm earth all the way through the house or even around the house from CU to the MET.

A simple solution would be to make this part of the house TT (the outside wall is only 2 metres away).

Would this be permitted?

Note: Gas and water bonds currently are only connected to the original CU.
 
How have you determined that the CPC is undersized ? It works out in most situations, that's why they put that size CPC in the cable.
 
work out your fault current then apply the adiabatic equation. from what you say in the OP, the bonding is alrteady in situ and i assume it;s 10mm. or could you install 10mm cpc to connect to the gas and/or water if it'ds close to CU2, thus combining cpc and bonding for CU2?
 
Hi Guys
Thanks for your replies.
1. This cable carries the main earth for the extension installation. As such, Table 54.7 could apply. For line conductors smaller than 16 sqmm, the protective conductor has to have at least the same cross-sectional area.

2. Is my adiabatic calculation correct? k=115. PFC at the DB is 1.3 kA. Fig 3A2(b) suggests t=0.1 for a BS3036 45 amp fuse. This gives 3.57 sqmm for the earth conductor. So 4 sqmm is ok? Though not exactly best practice?

3. The regs suggests that you can use the size determined by the adiabatic equation or the minimum value in table 54.7. The OSG only has the table, which is why I thought the earth was too small.

4. Where in the regs does it say that the earth and the main protective bonding can be combined? I could do this, but it would seem to me to be very bad practice. The stopcock is quite close!

That's all.

Pete
 
4. Where in the regs does it say that the earth and the main protective bonding can be combined?

where in the regs. does it say they can't? if you think of a sub DB (e.g.to an outbuilding)fed by a 3 core SWA, the earthing and bonding conductors are combined in the 3rd core. at the end f the day. it's all just an equipotential zone.
 
Hi Pirate - just my thoughts (and apologies if I'm wrong) but if this 2nd installation 'some way away' and if it has metal gas and water pipes entering the area, they should be bonded to that installation's board and not rely on the bonding done elsewhere? What do you think? Cheers, David
 
Nothing wrong with selecting from T54.7 but you cant fail a existing install without proving conductor doesnt meet adiabatic equasion. Adiabatic =3.57mm. So 4mm is adequate cpc. Bonding would need to be ran back to MET or EMT in main db01 providing earthing conductor to that db is correctly sized.
 
On the changing to TT question, I would not change earthing systems within the same building. But that's just me. Back to bonding conductors - having thought 4mm OK, I read chapter 5, section 544 Protective Bonding Conductors, first para 544.1.1 saying "Except where PME conditions apply, a main protective bonding conductor shall (!!!) have a cross sectional area ... and not less than 6mm2" . Am I reading that right? Cheers
 
If the cpc in that 10.0 T&E is to support main protective bonds then it is undersized. You will either have to put in place a TT earthing system or install a separate 10.0 cpc. GN8 figure 5.16 shows an example of this.
 
Thanks Guys for all your replies and discussion. I'm going with the adiabatic. It's not being used to support bonding. That has been done correctly at DB1.
Combined earth/bonding ok provided cable size is adequate. I did have a chat with the NICEIC support guy as this raised some issues I hadn't come across before. No probs.

TT and TNCS in same building - possible but bad practice.
 
On the changing to TT question, I would not change earthing systems within the same building. But that's just me. Back to bonding conductors - having thought 4mm OK, I read chapter 5, section 544 Protective Bonding Conductors, first para 544.1.1 saying "Except where PME conditions apply, a main protective bonding conductor shall (!!!) have a cross sectional area ... and not less than 6mm2" . Am I reading that right? Cheers
Correct, but 10 mm bonding already in place to DB1
 

Reply to Main Earth Problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main...
Replies
15
Views
866
Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
545

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock