as a little aside to the rights and wrongs of what to enter
RCDs and Indirect Contact Shock Protection
Indirect contact protection by fuses or circuit-breakers is dependent on the earth loop
impedance being within the parameters laid down by BS 7671. Where this cannot be
achieved or where there is some doubt about the consistency, then an alternative method
is required. It is in this situation that the residual current device can offer distinct
advantages over conventional overcurrent protection for indirect contact shock
protection.
The basis of RCD protection in this situation is to ensure that any voltage, due to earth
fault currents, that exceeds 50V is immediately disconnected. This is achieved by choosing
an appropriate residual current rating and calculating the maximum earth loop impedance
that would allow a fault voltage of 50V. This is calculated by using a simple formula given in
BS 7671 Regulation 413-02-16.
Zs x IΔn ≤ 50
Where Zs is the earth fault loop impedance (ohms)
IΔn is the rated residual operating current of the RCD (amps)
therefore a simple calc to arrive at the max zs is
zs = 50 (volts) / rated residual of rcd say for this example 30 ma
therefore max zs for a 30ma rcd (not time delayed) is max zs = 50 / 0.030 = 1666.67 ohms
although as some have said I would not be walking away if the zs reading was anywhere near that, nobody should