And that's an informed common sense approach that I will also continue to adopt.
This 1667 as a maximum permissable Ze is IMO a very dangerous approach. Sure the calculations stack up in theory, but in adopting these figures you are going down the slippery road of becoming totally reliant on the reliability of the RCD.
A possible way around could be to put more emphasis on the importance of the R1 + R2 readings rather than max Ze.
But when you have maximum Ze's permissable as 1667 in black and white, there really is nothing to stop the less informed from pointing a finger at that statement and saying , sorry but its within the value stated. End of.
Someone is going to die as a result of a failed RCD one day, and suddenly you will see 1667 disappear and the whole situation/regulations re-written as a result.
A lot of truth in what you say....however it rather ignores TT systems in which you are reliaint on RCD's for earth fault protection in practice....unless you go down the road of multiple linked electrodes to achieve a low enough Ra to operate an overcurrent device....IMO not practical in the majority of TT installations,and reliant on consistant ground conditions after initial verification. IMO the way to address this is more than one RCD ,ensuring discrimination.
Re the highlighted section of the quote....IMO as far as TN systems go,nobody is actually adopting the 1667 figure,it is a purely theoretical figure and technically the correct figure.....It could be argued that filling in the max figure for the overcurrent device on the cert is incorrect,as the 1667 is the maximum permitted.