hi guys

ive got myself a little confused here when trying to calculate a max demand figure for the installation below.

60amp TNCS supply to a bungalow.

1x 30A Ring Main
1x 30A cooker unit(with socket)
1x 40A Shower (8.5kw)
2x 20A Radials
1x 5A Lights (7x100w)

using table 1B app 1 OSG

ring main (30a) no diversity = 30A
cooker unit(30a) 10A+30%(fl)+5A =24A
shower(40a) no diversity = 36.9A
radial(20a) 40% = 8A
radial(20a) 40% = 8A
lights 66% =3.04A

using these figures it comes out at 109.9Amps what am i forgeting as this cant be right can it? do i have to apply diversity again ?

when i use my usual method of adding up the MCB's and then multiplying by 0.4

40+30+30+20+20+5 x 0.4 = 58 Amps

which is what id expect. any help would be appreciated.
 
the only thing i can think of is that i need to multiply the 109.9 x 0.4 (rule of thumb) but OSG does not mention this. im confused as i expected both methods to produce similar figures.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Maximum Demand/ Diversity
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
1
Unsolved
--

Advert

Thread statistics

Created
ianphilip007,
Last reply from
ianphilip007,
Replies
1
Views
2,235

Advert