hi there

i currently have a 6 way wylex NN board which has a 63A BS4293 RCD main switch. The MCB's are BS3871 Type 2 and 3.

would any new circuit added to this board be non compliant ? and therefore fail a Elecsa or any competent person assessment?

basically does the board need to be changed before i can add new circuits ?

many thanks
 
Does the RCD operate correctly at x1 and x5, and ramp test. Is it a 30mA RCD.

They're not manufactured any more but that doesn't mean they aren't fit to work!

Confirm the RCD works with an RCD tester.

Do you mean you have space on that old board and want to add an old MCB to it?
 
rcd is not 100ma it is 30ma and yes its trip time at x1 and times 5 are within spec. Ramp test is fine too.

i have a spare way with an exisiting 30Amcb in the exisiting board and wanted to run a new circuit.
 
I can't see any reason for not adding a new circuit to the existing board as long the RCD is still operating correctly like you have said.

SPARTYCUS has highlighted the obsolete bit.

Dont forget your bonding etc and highlight on the EIC re the main switch (RCD)covering the entire installation (Cant think of the word I am looking for)
 
just want it to be right for assessment and have these niggling little problems that i know my self are not ideal ie (rcd main switch and the old nature of the rcd and mcb) evrything else is to the 17th its just a pretty important part mainly fault protection and rcd protection thats not ideal. now if i note the niggles as limitations or deviations from BS7671 is this enough just dont want to fail due to niggles that i know are there.
 
Sorry you have lost me with 513 Accessibility. LIM is for PIR' s only!

It should make no difference if it is you assessement just make sure all the work you do is per the regs and you will have no problems at all!
 
If you're not a member yet and are thinking of using it for your assessment, I'd recommend calling Elecsa and running it past them.

They don't bite and I always find them helpful.
 

Reply to need some advice re current CU in the Australia area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Morning guys, I would like some advice, currently at my workplace, I am replacing a DB and existing wiring in a warehouse. One of the ways feeds...
Replies
4
Views
1K
Hi there. I’m hoping for some advice. I currently run a small limited company that provides IT services, both commercial and domestic so I...
Replies
0
Views
631
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock