Hi guys, Iv'e just qualified as a sparky and I'm going to rewire my friends house that he is renovating. I'm wondering if someone could clear up a couple of questions please.

1. The supply is a TT system with a earth rod out the back, the previous owner had a boiler fitted so the earthing was upgraded. The electrician has run 2 x 16mm earth cables up to the C/U. one goes direct to the earth rod and the other runs from the gas meter. The earth rod is right next to the gas meter so I thought I could go from the gas meter to the earth rod and to the C/U. Is this correct or does it need to go all the way to the C/U.

2. Checking the on site guide it shows cable run's up the corner of wall's, along the top of the wall's and horizontally at 150mm, but can I run the cable along the bottom of the wall's, behind the skirting as the house is concrete floors.

3. Just to confirm I have bought a BG split C/U with twin 30ma RCD's, This will be OK on the TT system..?? won't it. going to cross bond all the boiler pipes and bathroom pipes.

Any info would be great as I'm still learing.

Regards

Steven
 
Unbelievable.........................
 
You are going to have to learn a lot more.
1.)No, you cannot use the earthing conductor as a protective bonding conductor.
Why 16mm?
2) Safe zones. Check them out. If the sockets/accessories are at the same level, then yes, but you cannot really put them that low - Part M building Regs, so no, dont think about it.
3)Yes, that CU will be fine if plastic cased. Why cross-bond?

Are you sure you are competent to do this work? From these questions, it appears not. What will you do for testing before you energise the circuits?
 
steven don't take this the wrong way but you really shouldn't be learning how to wire an house without some help , from the basic questions your asking it is clear you are not competent enough to be doing the work , so do your friend a favour and don't do the job .
alanl beat me to it but same advice
 
My goodness. Please ask a competant spark to show you the ropes as this is quite shocking.
 
How can you have qualified as a spark but not even know the difference between "Earthing" & "Bonding" !
 
Well this is what has become of the domestic side of this trade a joke!!!
 
How can you have qualified as a spark but not even know the difference between "Earthing" & "Bonding" !

I agree...........so james............do you earth or equipotential bond or supplementary bond the armouring of swa cable when it has an integral earth/cpc core...............that is the question:).
 
you need to go back to college then Allan..
the one where he went....


"the one where he went".............depends which 'he' you were on about mate? lol.
No more college for me tho............combined cpc/bond and integral earth rubbish..........it's not allowed anymore seemingly and I just want to be put out to roost on gardening leave:)
 
  • Like
Reactions: 1 person
"the one where he went".............depends which 'he' you were on about mate? lol.
No more college for me tho............combined cpc/bond and integral earth rubbish..........it's not allowed anymore seemingly and I just want to be put out to roost on gardening leave:)
the one who posted that trash at #1...
 
Which thread :)
lol....

:50:

anyway...
how about some workgear for female sparkys..
direct from aldi:



W3013_TH_Sunday_15.jpg
 
  • Like
Reactions: 1 person
Hi guys, Iv'e just qualified as a sparky and I'm going to rewire my friends house that he is renovating. I'm wondering if someone could clear up a couple of questions please.

1. The supply is a TT system with a earth rod out the back, the previous owner had a boiler fitted so the earthing was upgraded. The electrician has run 2 x 16mm earth cables up to the C/U. one goes direct to the earth rod and the other runs from the gas meter.The earth rod is right next to the gas meter so I thought I could go from the gas meter to the earth rod and to the C/U. Is this correct or does it need to go all the way to the C/U.Well in theory it doesn't matter where the MET is, so yes the rod could be your MET. In which case the conductor to the cu is fine as is the conductor to the gas meter ........?


2. Checking the on site guide it shows cable run's up the corner of wall's, along the top of the wall's and horizontally at 150mm, but can I run the cable along the bottom of the wall's, behind the skirting as the house is concrete floors. A non starter ..................sorry!

3. Just to confirm I have bought a BG split C/U with twin 30ma RCD's, This will be OK on the TT system..?? won't it. Yes if installed right it will be fine
going to cross bond all the boiler pipes and bathroom pipes.Read the regs .............it might not be required:wink_smile:

Any info would be great as I'm still learing. You missed the N in learning....we are all still learning so ignore the pontificating individuals!

Regards

Steven
>>>>>>>>>>>>>>>>>>see my reply in red & sorry if I offend
 
Hi guys, Iv'e just qualified as a sparky and I'm going to rewire my friends house that he is renovating. I'm wondering if someone could clear up a couple of questions please.

1. The supply is a TT system with a earth rod out the back, the previous owner had a boiler fitted so the earthing was upgraded. The electrician has run 2 x 16mm earth cables up to the C/U. one goes direct to the earth rod and the other runs from the gas meter. The earth rod is right next to the gas meter so I thought I could go from the gas meter to the earth rod and to the C/U. Is this correct or does it need to go all the way to the C/U.

2. Checking the on site guide it shows cable run's up the corner of wall's, along the top of the wall's and horizontally at 150mm, but can I run the cable along the bottom of the wall's, behind the skirting as the house is concrete floors.

3. Just to confirm I have bought a BG split C/U with twin 30ma RCD's, This will be OK on the TT system..?? won't it. going to cross bond all the boiler pipes and bathroom pipes.

Any info would be great as I'm still learing.

Regards

Steven

Haha best joke I have heard in ages!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Newbie needs some help please
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
18

Advert

Thread statistics

Created
steven9586,
Last reply from
ChrisElectrical88,
Replies
18
Views
1,896

Advert