Are you sure? That is a very odd cable to use for a domestic installation these days considering it costs around £10/m
I'm not sure whether its MICC but I attach an image of what they've run to my hut. None of the cable is exposed to the elements.
micc.jpg
 
Looks like rubber flex to me. Can you show a larger section in situ.
 
  • Like
Reactions: DPG
Looks like rubber flex to me. Can you show a larger section in situ.
Thanks for getting back so quickly. I attach another image. My sparky is coming back tomorrow to hook up the CU
micc1.jpg
 
I'm not sure whether its MICC but I attach an image of what they've run to my hut. None of the cable is exposed to the elements.
View attachment 53750
Not MICC then, was this cable circular before you split it to show it's construction? or was it flat?
 
Are the copper cores solid, stranded or multi-stranded.
 
  • Agree
Reactions: Pete999
Not MICC then, was this cable circular before you split it to show it's construction? or was it flat?
Thanks for reply. The cable is circular
 
  • Like
Reactions: Pete999
I go with Dave then in #23 It is NYY-J.
 
No it is NYY-J commonly known as Hi-Tuff.
 
  • Agree
Reactions: ipf and Risteard
Just a big thank you to you all. I know "a little knowledge is a dangerous thing" and having a little knowledge would certainly apply to me, but I'm still learning and you guys help greatly.
 
  • Like
Reactions: westward10 and DPG
Either way Hi-tuff has not got an earthed metallic covering (like SWA) so it will need to be protected at source by an RCD like he has. Just not ideal its attached to the same RCD thats covering some of your house circuit's
 
  • Agree
Reactions: ipf
Hi-Tuff is a good alternative to swa in some circumstances.
Question is, is the cable being run underground to the shed? If so, it's not an option, due to insufficient protection.
How old is the consumer unit? Is it possible to alter and feed via RCBO?
 
  • Like
Reactions: AJshep
Hi-Tuff is a good alternative to swa in some circumstances.
Question is, is the cable being run underground to the shed? If so, it's not an option, due to insufficient protection.
How old is the consumer unit? Is it possible to alter and feed via RCBO?
Thanks for replying. The cable is cleated to joists through my shop store to the shed attached to the shop store. At no point is it underground. As in the OP, the consumer unit fitted by my sparky is a brand new Hager 10 way dual RCD
 
Thanks for replying. The cable is cleated to joists through my shop store to the shed attached to the shop store. At no point is it underground. As in the OP, the consumer unit fitted by my sparky is a brand new Hager 10 way dual RCD
OK, then.
As regards the Hager, I'm not positive, but would think it's possible to create a non RCD protected section. 20/32 amp RCBO should be fine.
 
Either way Hi-tuff has not got an earthed metallic covering (like SWA) so it will need to be protected at source by an RCD like he has. Just not ideal its attached to the same RCD thats covering some of your house circuit's

That doesn't necessarily mean it needs to be protected by RCD.
This would only be required for the cable if it was chased in to a wall at less than 50mm deep, so if it is clipped direct as it appears then its not needed.
 
  • Agree
Reactions: AJshep
That doesn't necessarily mean it needs to be protected by RCD.
This would only be required for the cable if it was chased in to a wall at less than 50mm deep, so if it is clipped direct as it appears then its not needed.
Agreed. For some reason I was under the impression it was buried.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Scotland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
No RCD in sub main
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
37

Advert

Thread statistics

Created
KeenPensioner,
Last reply from
AJshep,
Replies
37
Views
8,930

Advert