Just returned from callout to Old dear in village who had a problem with an RCD tripping. Checked circuits and discovered that she had just connected 3 oil filled radiators to ring circuit to "keep chill out" before having to use central heating. Oil filled radiators have not been used for 6 months. 2 of the 3 are causing the RCD to trip. Has anyone come across this?
Possible cause is there is a fault on the radiators thats why RCD is tripping
I checked out the earth bond and insulation with a PAT. Failed on both. As I was curious I connected both radiators to a circuit not protected by RCD for 2 minutes. Carried out PAT again. Passed this time. Connected them to RCD side again. Operated normally. Have taken them away to remove the temptation to use them. They are currently running in my workshop on a test rig so I can monitor them.
Reply to Oil filled radiators tripping RCD in the Industrial Electricians' Talk area at ElectriciansForums.net
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...