Hello everybody,

I have a few questions, which I would appreciate any answers to.

Firstly, for a radial circuit, single socket, with 2.5mm cables T&E about 2 metres long, just for general domestic use in a hallway, what rating of type B circuit protective device would you recommend?

Secondly, for a door bell transformer, would you recommend that I put it on an existing circuit such as the lighting circuit? or put it on an individual circuit?

Thanks in advance guys
 
Hello everybody,

I have a few questions, which I would appreciate any answers to.

Firstly, for a radial circuit, single socket, with 2.5mm cables T&E about 2 metres long, just for general domestic use in a hallway, what rating of type B circuit protective device would you recommend? 16A or 20A.

Secondly, for a door bell transformer, would you recommend that I put it on an existing circuit such as the lighting circuit? or put it on an individual circuit? Put it on with the downstairs lights not really worth a circuit all to itself.


Thanks in advance guys

In blue.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Old CU replaced with new 17th edition
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
P&Q,
Last reply from
P&Q,
Replies
3
Views
1,219

Advert