But the circuit doe snot have RCB protection...I thought a MCB would not trip from simply a live to earth fault - wouldn't you need an RCB or RCBO? thanks
It depends on the type of Earth, but as long as >6A fault current can flow from L to E, it can still trip an MCB!
But as stated above, it is likely to be more than simply damp (which would trip an RCD @ 30mA, but likely wouldn't run to anything like enough to trip an MCB)
 