D
davesparks
Looking at the gas bottle store, It will be very easy to disconnect earth links between gas pipes to the other house and the separation between the pipes is around 1.2m. the gas bottles themself cannot easily touch the others and they are also connected via rubber hoses. Will this be enough separation in the ground, I could do a resistance test between the gas pipes for the other houses.
Also I do minor works certs for the work I do on my house, would a minor works certs for changing to TT do, and if so the format of a minor work cert doesn't lend its self to this, so what documentation could be better instead
Don't disconnect the bonding between the gas pipes, you'll have two different earth potentials within close proximity of each other.
Like it or not you are stuck with those bonds being in place and these various connections to the PME earth.
No a minor works certificate isn't appropriate for changing the earthing arrangements of the entire installation in my opinion, a full EIC should be issued with all circuits fully tested.
[automerge]1586987417[/automerge]
It looks as if I should be able to get earth rod resistance down to around 15-20ohm using 2 rods and the gas pipe
Can you clarify what you mean by two rods, how long are they and how far apart?
You cannot use a gas pipe as an earth electrode, so don't factor that in to any calculation. Of course the problem with that is you can't stop fault current flowing through the gas pipe whatever the regulations say, and if it is in good contact with the ground it will have a low Ra of its own whatever you do.