Would any fellow electricians consider using an open PEN device to protect a metal trailer used as a "Canteen". It is likely to be often connected to TNCS (forbidden by 717.411.4) and placed on concrete which makes the use of TT and rod impossible. I can draw similarity to an EV charge point with open PEN limiting the touch voltage on the car it's charging. Is this a viable option or am I missing an obvious danger that this might create. My thinking is that the user of the trailer will not be concerned with the type of supply and would connect regardless.
Your comments and thoughts would be most welcome.
I asked the Technical helpline of my registration body and got 2 different answers, this was obviously really unhelpful !!
 
Interesting. First things first - a common misconception is that you need to have an earth rod adjacent, you don't - it could be a distance away so consider if a 'remote' rod and cable run (adiabatic ahoy!) might overcome this by conventional methods first before going off-piste.

If you're still stuck, then engineering principles take over and BS7671 makes allowance for using 'new' technology or alternative methods to achieve at least the same degree of safety. However, first consider whether by bonding the trailer in the first place (which I assume is what you're getting at) if you're potentially creating a danger via introducing an earth path where none previously existed - only you know what you're looking at.
 
These open PEN devices have been specifically designed for EVSE to overcome the difficulties of implementing safe TT systems derived from PME sources which can include TN-S, it requires more consideration that just banging an electrode in. Personally I would not consider it.
 

Reply to open PEN protection. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

As the title says, does a three-pin socket (external) used as charging point need an earth electrode or open PEN fault? Are mode 1 and mode 2...
Replies
17
Views
5K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
I have been asked/invited to "post more", lol, so let me make another post right away. I thought of sth worthy to post, of interest to many, I...
Replies
1
Views
439
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
The situation is: Power is needed inside a greenhouse to power a specialized greenhouse heater, a timed motorized window opener and a light. The...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock