Because I have no idea how deep the structural steelwork is. It is only a car port, not a major building, so any depth to the structure might only be 0.5m or less! So no idea if it would remain low R all year so might not meet regulation 542.2.4Why do you say they 'ought to have' a rod in addition to buried structural steelwork? There's nothing in the regulations to support this statement.
Regulation 411.5.3 Table 41.5Why does it only need to be below 200 ohms? There's no regulation which says that and it makes no technical sense to use 200 as an upper limit.
Note 2 in relation to RCD of 30mA and 100mA where the limits are 1667 and 500 ohms respectively states that "A value exceeding 200 ohms may not be stable"
[automerge]1587038691[/automerge]
So yes if there was talk of a 300mA S-type RCD it would need to be lower (167 ohm or less, but earlier it was a 100mA S-type discussed), and it is always best to be as low as practical, but my point was if you discount all other fortuitous earthing due to buried metalwork that you have little or no information about, a known deep earth rod that meets the minimum for the RCD and is low enough to be considered stable stable would guarantee it meets the disconnection requirements.