As others have said, it's the cable insulation breaking down.
Had one at home many years ago, occasional load bangs & blown fuse.
Eventually there was an almighty loud bang, saw the flash through the gaps in floorboards, circuit fuse intact, suppliers fuse blown. Cable totally destroyed!
This was just a cable clipped to the underside of the ground floor joists.

Probably time to get an electrician in, unless of course you're capable yourself. :)
 
might not be insulation breakdown . could be a fractured conductor arcing.
 
Time for a bit of testing , if it has stopped when you have disconnected that circuit you have a problem that needs sorting PDQ.

If you have no test equipment it will be difficult to do yourself. You have a head start , at least you know what area it is in and which circuit it is. If the wire is in the cavity and you can hear it , it's one loud pop.
 
I had a customer with the same problem just a few months ago. A hell of pop!
Found it behind the skirting - chewed by a rat!
4ebanepy.jpg

jasu3y9e.jpg

nevasapu.jpg

ysyhy6y4.jpg
 
Same as post 17.

One time it was rat damage behind kitchen units and the second was from some crap work by someone else who had clipped the insulation of the cable when clipping to the wall.

On both occasions, the presence of damp made it worse.
 

Reply to popping noise from wall in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi All, Wondering if I can get some advice. Basically I’m having exposed joist ceilings in my house and I’m in the process of slowly changing all...
Replies
5
Views
1K
Hello I notice a strange intermittent noise which seems to come through the party wall of my neighbour. It appears to originate from their...
Replies
10
Views
1K
Rewiring an old farm cottage… every wall brick and previous wiring not done well at all. I can’t locate any of the prescribed zones diagrams on...
Replies
12
Views
2K
This evening my partner and I were sitting on the couch and heard a very loud sudden “pop”. It sounded like it came from the corner of our living...
Replies
1
Views
12K
An odd question granted but bear with me. I've got to extend a radial circuit in a community centre to fit a new hand dryer in the toilets, but I...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock