Hi

I have a question with regards to connecting two different earthing systems.

I am on a vessel which has a switchboard set up that is TN-C, combined neutral earth, this is supplied by onboard gensets, 3 Phase 380V 50 Hz.

With regulations as they are all boatyards/docks are set up with a sperate earth and neutral supply for the vessels docking there.

So I need to supply the vessel with shore power while both generators are shut down for Maintenance, therefore connecting a seperate earth neutral supply to a combined earth demand.

Obviously if the combined earth neutral from the vessel is taken directly to the vessel then it causes the power supply to trip.

I was wondering if ther was any safe way to connect these two systems without leaving risks of high fault currents.

Is it possible to bond the earth to the hull of the vessel as this is steel and take the combined leg directly to the neutral? Or is there any way to combine the neutral/earth supply before it reaches the vessels switchboard?

Or are there any products that can be used to help make the link up possible?

Thanks for any advice

Andy:confused:
 
Last edited by a moderator:
morning andy and welcome to the forum. i'm sorry but this is beyond my range of experience, hopefully one of the others here can give you the answer you need. good luck
 
Not my area of experience at all but wonder if the solution was to install an isolating transformer on the boat for the yard supply to connect to, then connect the boat to the output of the transformer?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Query on Protective Multiple Earth
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
andy_b,
Last reply from
ghost,
Replies
6
Views
2,541

Advert