Discuss R1 + R2 expected readings in the UK Electrical Forum area at ElectriciansForums.net
The place I work also tells us we are NOT to work live.
Dunno how the hell we're supposed to complete EICRs.
Odd. There is working live and working LIVE.
Originally I assumed that "working live" was the sort of high-risk activity such as making a change/repair to an energised system, you know the really squeaky-pants time and not something you would ever do unless there really was absolutely no alternative.
But of course any energised testing is also "working live" and then it gets more complicated as typically EICR and EIC both requier measurements such as Ze and Zs to be done, along with RCD trip-testing. Just how much exposure is too much to be safe?
  • Do you base it on where you test (i.e. the CAT-II final point versus CAT-III DB location idea)?
  • Do you base it on available arc-flash energy?
  • Do you base it on whether it is done via probes or a 13A socket?
  • If so do you leave light circuits untested, so the owner/occupier is the first one to encounter a problem?
No someone has decided live not safe, simple as that.
@Lt1990 is only carrying out works in the way as suggested by his company.
Obviously.
I wasn't castigating the OP more the company.
I think regulation 14 and a) b) c) have been interpreted extremely tightly. The observation was more that there is no real life measurement for compliance with ADS and I conclude the risk associated with that is higher (unreasonable) (even within reg 14) than the reasonable test. It may well be the insurers have said if anyone works live we will not cover you, end of. But as a tester you might also apply "reasonable" to your own tests. I am not working near a live conductor. Any such conductors are enclosed i.e. in a socket or ceiling rose if I use the lightmate (kewtech) Testing sockets with the plug adaptor if seen as a risk then puts the idea of plugging in any appliance could also be seen as a risk due to "working live" and as a BA1 person plugging in the hoover....
It’s an interesting discussion.
I can think of countless times where live Zs has been lower than Ze+(R1+R2), some TT cases where parallel paths have even thrown it into TN level readings.
I’m trying to remember if I’ve ever had one read worse and I’m not quickly coming up with a scenario where that is in fact possible (resistances in parallel formula). Any ideas?
What I do like about the live Zs test is that it serves as a final check that everything I’ve disturbed for testing has been put back together adequately!
I work a lot under some of the most insanely rigid health & safety rules imaginable. Don't want to go into details, but you couldn't make some of it up. Of course they forget all about those rules, when processes trump safety, and have you working in live busbar chambers.
Unlike me, here's a controversial thought....
As the company are apparently happy enough with pushing GS38 probes into a stationary main switch for a Ze, it would be interesting to know what they made of the Zs trick in the Kitcher book.
I've mentioned this more than once before, but it doesn't seem to be commonly known or used, so I'll bore people again:
Lock off circuit.
Prove dead at furthest point.
Add temporary link between R1 and R2 at furthest point.
Do 2-wire high current loop test between a live source (bus bar or top of main switch) and the top of the locked off and open breaker or RCBO.
Remove link (or take a jump backwards when breaker jumps straight back open having proved ADS works a 2nd way 🤣)
This is extending the CPC back from the end of the circuit to the CU using the live and allows a more accurate high current loop test.
Everything stays in terminals the board end.
Everything is dead at the point the difficult end is exposed and worked on.
It's only not-dead for the very short duration of the actual high current test.
If they allow Ze and RCD tests I can't see why they wouldn't allow this. You'd also have more accurate live Zs results than anyone else!
Just shows you what matters with a bit of financial pressure. Frightened $hitless when it comes to a loss of profit. Actually, that's one of the main reasons for H+S, to prevent pay outs, but when it comes to the crunch, they gamble.
Reply to R1 + R2 expected readings in the UK Electrical Forum area at ElectriciansForums.net
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
OLDBOY
O
Today I was doing an EICR and went around a couple sockets with a Megger MST220 socket tester just to see if there was anything obvious, all three...
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
hi all just got a Q regarding how to find R1 then second Q how to find R2 what i did so far was mutiplying each answer for1.67 so I could get the...