Testing SWA 16mm sub main to a garage, getting reading of 66 ohms between R1+R2 and a IR resistance of between 4-5 M Ohms anyone explain how? The RCD is all fine and not tripping just testing
L
All I can think of is loose connection one end, high resistance joint, or SWA corroded
 
is the armour used as cpc or is there a separate conductor in the cable?
 
combination of damp and corrosion oerhaps. open up the glands and check them.
 
What is the R1 + Rn?

If that matches the resistance one calculates due to length, then it's almost certainly a bad joint armour to gland or gland through to your test point.

So short one end and test between L and armour at the far end, then swap round end to end etc to narrow it down
 
What is the R1 + Rn?

If that matches the resistance one calculates due to length, then it's almost certainly a bad joint armour to gland or gland through to your test point
I’ll test that, and I’ve re tested and it’s still 50-60 ohms R1+R2 but I’m getting nearly a dead short between L-N 0.5 M Ohms and L-E which is just higher than 1 M Ohms
 
New or existing cable? Can you inspect along the run for damage?
 
If this is an EICR then I would FI and move on.

High R1+R2 could well be stopping the RCD from tipping.
 
nearly a dead short between L-N 0.5 M Ohms and L-E which is just higher than 1 M Ohms

Megohms? A dead short is typically a reading of an ohm or two, due to conductors touching together. Your reading is a million times higher than that, so it's just low insulation. Still high enough to work fine (creating less than half a milliamp of leakage) but not as high as you would expect or want to see and therefore a possible pointer to a damp or damaged cable.

The term 'short-circuit' is oft abused, but it specifically means that the insulation is completely breached by effectively zero resistance, so only the conductor resistance is present. Even if an insulation test reads 0.00MΩ it's not a cast-iron guarantee that a short is present, as it could still be 10kΩ which represents a small load (and still too high to trip an RCD by itself.)
 
my procedure would be to undo the glands at both ends, separate the cable from the glands and test the cable itself to find or eliminate the fault/s.
 

Reply to R1+R2 high but IR low in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
876
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
609
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
728

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock