olsonn

Hi

After a bit of advice ahead of my practical exam on Wednesday. When RCD testing on a split board which has socket circuits on both RCD's do I need to also test lighting circuits or will testing at 0.5x 1.0x and 5.0x at the sockets suffice. Everything I read shows the tests being undertaken on socket ring circuits and nothing on radial lighting circuits
 
you only need to test each RCD once. either at a socket or at the RCD itself. a lot of us prefer this way as with the associated MCBs OFF, the circuit will not affect the test. ( something plugged in, or light fittings can give weird results.)
 
I agree with telectrix first post. Also just to add, GN3 says that loads should be removed when carrying out an RCD test. We had a thread a couple of months ago where a sky+ box was unfortunately no longer working after an RCD test had been carried out on the circuit it was connected to.
So isolating MCB's and testing on the load side is a good guaranteed method of assuring this does not happen.
I have however experienced a Mr NICEIC man say that I should only test it at the socket as it is a live test and they bring up EAW Reg 14, I argued it with him and he conceded.
 
Last edited:
I was once told thats how the niceic guy wants it, he wanted to see the rcd results on each cct.
But I aways test with the mcbs off at the actual RCD unit, and write the results as if I had tested the RCD on each of the ccts.
 
I was once told thats how the niceic guy wants it, he wanted to see the rcd results on each cct.
But I aways test with the mcbs off at the actual RCD unit, and write the results as if I had tested the RCD on each of the ccts.

obvoiusly, the niceic guy's a jobsworth. reading wrfitten on 1st cct. then dittos under, is what i do.
 
I was once told thats how the niceic guy wants it, he wanted to see the rcd results on each cct.
But I aways test with the mcbs off at the actual RCD unit, and write the results as if I had tested the RCD on each of the ccts.

Don't worry, your NICEIC chap will be happier that you knew to perform the test once correctly.
 
I agree with telectrix first post. Also just to add, GN3 says that loads should be removed when carrying out an RCD test. We had a thread a couple of months ago where a sky+ box was unfortunately no longer working after an RCD test had been carried out on the circuit it was connected to.
So isolating MCB's and testing on the load side is a good guaranteed method of assuring this does not happen.
I have however experienced a Mr NICEIC man say that I should only test it at the socket as it is a live test and they bring up EAW Reg 14, I argued it with him and he conceded.

Widdler, don't you just love continuity - My Mr NICEIC made me test at the board on the RCD itself! :)
 
Hey,
I have just done my practical exam today (2330 lvl 3). I had to test a split load board, and test one rcd using the probes on the lighting circuit and the other rcd using the sockets, 1 manual and the other automatic.

Hope that helps a little.
Cheers
Ash
 

Reply to RCD Testing on a split board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
379
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
860
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
309
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
933
Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Replies
5
Views
819

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock