The N-E 'fault' is most likely the N-E loop of a TN-C-S installation. If you're not an electrician, with TN-C-S you have a line conductor and a neutral conductor coming in to the service head. The earth is then linked to the neutral conductor. TN-C-S stands for Terra Neutral Combined Separate as in earth/neutral combined (in the cable) and then separate (at the service head).

On the consumer side, if the installation is not fully isolated you will get a continuity reading between earth and neutral which is why you should fully isolate circuits for this kind of fault finding.
Will happen on TN-S also as neutral and earth connected at the star point of the transformer :)
 
Thanks SparkyChick ... I drew the line when I have to open up my consumer unit.
Maybe later in the year (can't believe June is coming to an end !) I will enroll in a course ,perhaps in November,and by Christmas I'll officially be qualified as an electrician to better protect my house !

btw, I had the electrician test my RCD again to make sure it is all working and it is.
Corrected that for you to be more realistic with current training requirements.
 
New posts

Reply to RCD trips a few minutes after lights turned on in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K
Kitchen led lights have all of a sudden dimmed by about 30% no dimmer in the system. There are 2 switches for this set of lights. Regardless of...
Replies
2
Views
833
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
848

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock