Discuss rcd in the UK Electrical Forum area at ElectriciansForums.net

There is an interesting article in jan PE mag on this...and it argues that a 100ma S type will fall foul of reg 531.2.9 re- ensuring downstream devices tripping before upstream in the event of a fault. The conclusion was a minimum of 300ma S type would be required for final circuits with 30ma protection.

100mA or 300mA it won't make too much of a difference on a TT system. So what was the argument put forward for a 300mA S type over a 100mA S type?? Level of fault?? I would think most actual fault levels, rather than an increasing combined leakage, will exceed 300mA as well... lol!!
 
Ok why a s type 100ma


why not?

The time delay will allow the circuit protected by the RCBO to trip first in a fault condition, it is also there as a back up should the RCBO fail, there are also some sparks (uhum, cough) who think a double pole main switch is the best way and individual rcbos after (cough) but there will be trouble suggesting it, ahem cough
 
No 1 can answer it can they
Yes they can.
With a TT installation, overload protection can be provided as with any other installation by a fuse or MCB.
However due to the High Zs in most TT installations, earth fault protection cannot be provided by such devices.
Therfore the options are to use an RCD, electrical separation, earth free location or double insulation.
As most of those options are not practical, or insome cases allowed in domestic installations, RCDs are used.

There is a requirement to divide an installation into separate circuits, so as to amongst other things minimise iconvenience in the event of a fault.
So we use a time delayed RCD which used to set so that it operated within 5secs, but now has to be set so that it operates within 1 sec.
100mA is used, to avoid nuisance tripping from combined earth leakage from multiple circuits.
10mA earth leakage on 3 circuits will not cause a 100mA RCD to operate, but would cause a 30mA RCD to operate.
Circuits that require 30mA RCD protection are then provided with such protection, and the 30mA earth leakage required to cause such devices to oper ate will not also cause the 100mA RCD to operate.
The reason why the 100mA RCD is time delayed, is in case of an earth fault causing a current greater than 100mA.
An earth fault of 100mA would cause wither the 30mA RCD or the 100mA RCD to operate, and ins ome cases both.
By delaying the 100mA RCD, the 30mA RCD will operate before the 100mA RCD has a chance.
Obviously an earth fault between the 100mA and the 30mA RCDs or on a non 30mA RCD protected circuit, will cause the 100mA RCD to operate.
 
So basically the 100ma protects not only final circuits if the 30ma fails it protects the distribution side ie fault occuring on meter tails and none rcd protected circuits.
 

Reply to rcd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
348
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
325
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock