Look on the relay and you will see a diagram in the form of a 2 way switch the common will have a number beside it ie 1 then the Normally Closed contact 3 Normally Open 2

Easy way to check is put a meter set for ohms or a bleep accross 1 and 3 (numbers should be marked on the relay base) and with the relay de-energised you should get a circuit now check 1 and 2 and you will not get a circuit until you energise the relay ie check the coil rating 24vac or 240vac if 240 then apply 240 accross A1 & A2 then you get a circuit accross 1&2 and no circuit on 1&3

Relays come in 2 versions 8 pole and 12 pole

8 pole is A1&A2 plus 2 sets of contacts
12 pole is A1&A2 plus 3 sets of contacts
 
Look on the relay and you will see a diagram in the form of a 2 way switch the common will have a number beside it ie 1 then the Normally Closed contact 3 Normally Open 2

Easy way to check is put a meter set for ohms or a bleep accross 1 and 3 (numbers should be marked on the relay base) and with the relay de-energised you should get a circuit now check 1 and 2 and you will not get a circuit until you energise the relay ie check the coil rating 24vac or 240vac if 240 then apply 240 accross A1 & A2 then you get a circuit accross 1&2 and no circuit on 1&3

Relays come in 2 versions 8 pole and 12 pole

8 pole is A1&A2 plus 2 sets of contacts
12 pole is A1&A2 plus 3 sets of contacts

that will work for a conventional relay, the op wants to check a solid state relay, no coil or moving contacts;)
 
pmac10 is correct. It runs off a plc 24v and makes a contact at the other end to connect 230v. There is no a1/a2 or n/o, n/c terminals just the 4 terminals. It has 24v going in but nothing coming out. Just wondered if there was a way to test if its faulty. Its a crydom solid state relay from RS rates at 2 - 32v dc.
 
pmac10 is correct. It runs off a plc 24v and makes a contact at the other end to connect 230v. There is no a1/a2 or n/o, n/c terminals just the 4 terminals. It has 24v going in but nothing coming out. Just wondered if there was a way to test if its faulty. Its a crydom solid state relay from RS rates at 2 - 32v dc.
i know the one you mean mate, the labels may have worn off, but if you can identify the two terminals which should have 24vdc across them, check you have it, if you do, thats your 'A1/A2' so to speak, coil energised. go to the other two terminals, you should have 230v to earth at, at least one terminal, your 230v in, if your 'coil' is energised, you should get 230v at the other, otherwise its no good.
semiconductor devices are either conducting or insulating. with no 24vdc at the upper terminals, the lower 2 are insulated from one another, with 24vdc present at the upper terminals the lower ones are in a conducting state:)
(as an after thought, if you have no terminals labelled, bear in mind you can mount these upside down:()
 
Cheers mate. The labels are ok and I have 24v at the bottom where its supposed to be but no voltage at the other end. Wouldnt mind but its brand new. Or well, Ill just order another and the company will pay for it.
Cheers for the feedback:D.
 

Reply to Relay in the Australia area at ElectriciansForums.net

Similar Threads

Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Replies
8
Views
584
Hello folks, So my van got found after being stolen ;D Now I'm installing my own alarm on the van which is triggered when a door is opened. Im...
Replies
4
Views
508
I have a customer that has 3 heating mats under the tile. This was installed a while back and a relay was used. I measured a 21 amp draw for all...
Replies
4
Views
2K
Hello all.. I have been asked to wire a relay into a FCU for a 3kW immersion. The plan is for the customer to be able to access the immersion...
Replies
17
Views
2K
I went to look at mess this morning. S plan heating system, google nest heat link in airing cupboard. Downstairs in utility room the kitchen...
Replies
5
Views
759

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock