I've been asked to go and price a job based on an EICR that the client has had done. Some strange coding in my opinion but just wondering what you guys think?:thumbsup
 

Attachments

  • ScreenHunter_01 Mar. 07 16.08.jpg
    ScreenHunter_01 Mar. 07 16.08.jpg
    201.4 KB · Views: 361
  • ScreenHunter_02 Mar. 07 16.08.jpg
    ScreenHunter_02 Mar. 07 16.08.jpg
    80.6 KB · Views: 198
  • ScreenHunter_03 Mar. 07 16.09.jpg
    ScreenHunter_03 Mar. 07 16.09.jpg
    125.4 KB · Views: 186
  • ScreenHunter_04 Mar. 07 16.09.jpg
    ScreenHunter_04 Mar. 07 16.09.jpg
    195.8 KB · Views: 197
  • ScreenHunter_05 Mar. 07 16.10.jpg
    ScreenHunter_05 Mar. 07 16.10.jpg
    214.9 KB · Views: 205
  • ScreenHunter_06 Mar. 07 16.10.jpg
    ScreenHunter_06 Mar. 07 16.10.jpg
    174.3 KB · Views: 182
  • ScreenHunter_07 Mar. 07 16.11.jpg
    ScreenHunter_07 Mar. 07 16.11.jpg
    168.8 KB · Views: 225
  • ScreenHunter_08 Mar. 07 16.11.jpg
    ScreenHunter_08 Mar. 07 16.11.jpg
    101.3 KB · Views: 170
Does not meet Redulations! a new Regulation of some sort? lol.

I suppose I better look over it properly.
 
Unidentified circuits put as Code 3 on observations but as Code 1 on Inspection, I could be here all day picking holes in this, blimey that is a badly filled report.
 
  • Like
Reactions: 1 person
Hi all, just to jump on the bandwagon, have a look at this certificate and let me know your thoughts, was a customer of ours who had this report done as part of their rental agreement on a posh estate in Highgate, Same firm prob does about 50 houses on the same estate.

Enjoy

SKMBT_22312030717540_0001.jpgSKMBT_22312030717540_0002.jpgSKMBT_22312030717540_0003.jpgSKMBT_22312030717540_0004.jpgSKMBT_22312030717540_0005.jpgSKMBT_22312030717540_0006.jpgSKMBT_22312030717540_0007.jpgSKMBT_22312030717540_0008.jpgSKMBT_22312030717540_0009.jpgSKMBT_22312030717540_0010.jpgSKMBT_22312030717540_0011.jpg
 

Attachments

  • SKMBT_22312030717460_0001.jpg
    SKMBT_22312030717460_0001.jpg
    234.1 KB · Views: 93
  • SKMBT_22312030717460_0002.jpg
    SKMBT_22312030717460_0002.jpg
    206.4 KB · Views: 86
  • SKMBT_22312030717460_0003.jpg
    SKMBT_22312030717460_0003.jpg
    338.8 KB · Views: 80
  • SKMBT_22312030717460_0004.jpg
    SKMBT_22312030717460_0004.jpg
    223.4 KB · Views: 80
  • SKMBT_22312030717460_0005.jpg
    SKMBT_22312030717460_0005.jpg
    218 KB · Views: 70
  • SKMBT_22312030717460_0006.jpg
    SKMBT_22312030717460_0006.jpg
    208.9 KB · Views: 72
  • SKMBT_22312030717460_0007.jpg
    SKMBT_22312030717460_0007.jpg
    88.2 KB · Views: 64
  • SKMBT_22312030717460_0008.jpg
    SKMBT_22312030717460_0008.jpg
    88.9 KB · Views: 63
  • SKMBT_22312030717460_0009.jpg
    SKMBT_22312030717460_0009.jpg
    95.2 KB · Views: 71
  • SKMBT_22312030717460_0010.jpg
    SKMBT_22312030717460_0010.jpg
    48.2 KB · Views: 60
  • SKMBT_22312030717460_0011.jpg
    SKMBT_22312030717460_0011.jpg
    73.3 KB · Views: 65
Unidentified circuits put as Code 3 on observations but as Code 1 on Inspection, I could be here all day picking holes in this, blimey that is a badly filled report.

Totally agree.

I only looked at the first page, it seems that whoever filled that report out needs to have a good read through the guidance notes for the codes. For example the "No RCD throughout installation" is down as a C1, or the C1 for the bathroom fan being 230v, the bit about needing a hammer and screwdriver (butcher!) to access the fuse board is a C3. To put it mildly the report is a load of nonsense, but probably contains some genuine (if incorrectly coded) issues.

The customer's not going to be happy about paying for another report though. I guess someone's going to get the ear bent, and hopefully reported to their scheme for being a muppet.
 
ADS on an old install ? Code 1's on a boiler cover, Code 1 for no rcd ? Identification of circuits Code 1 lol, Code 1 for cables concealed in walls ? Gas boiler not fixed Code 1 (must be a Gas Safe check too) Clip missing from a light Code 1, There's loads of crap on there. By the looks of it no one should be in the property with all that danger around. Someones looking for a nice wager by the looks of things

5s disonnection time for a 5/15 fuse ?
0.01 on end to ends ?

Throw that report in the bin
 
Last edited by a moderator:
Whoever filled that in is clearly an idiot that needs to go back to school, learn english, then go and learn to be an electrician again!
 
1short fairly poorly coded, written and explained EICR, looks like they may have done the testing at least but observations and tick boxes do not match up and codes are generally incorrect in my opinion.

A1G
can't read a lot of the report because of the background but what I can read does seem OK at first glance, slightly surprised there is 16mm bonding but could be someone being keen. The defect sheet is not part of the report and should not be included as part of the report. recommendations should be in a cover letter, not in the report.
The statement old MCBs may not work and suggesting an injection test must be pure conjecture, surely.
Codes are a bit odd and recommendations are also sometimes strange.
 
  • Like
Reactions: 1 person
fairly poorly coded, written and explained EICR, looks like they may have done the testing at least but observations and tick boxes do not match up and codes are generally incorrect in my opinion.

Whilst I am sure there are some very valid observations I do not believe that I'm going to be rubber suited to walk in there which is almost the impression I get when reading the report.

I think the person who conducted the test needs to remind themselves why a code 1 would be issued and what needs to be done when reporting a code 1.

Reading that report made me wonder why I have chosen not to provide this service yet lol Seems unlike this chap, I am aware of my limitations ;)

Thanks for your replies:thumbsup
 
Yeah, but from what the report says, the EEB bit is missing from this install :willy_nilly:

On a serious note, I thought that the terminology had changed and that putting ADS was acceptable these days??

As far as I was aware EEBADS is still used in older systems as thats what they are
 
All I can say is that the socket ring ring circuits must be VERY short based on those readings!!

Also looks like the IR test was performed using only a 250v test???

If a 100% inspection & test is required and the 250v test indicates that there are no faults then why no quickly test at 500v?

If/When I get the chance to pop over I'll take my camera and post up some pictures :thumbsup
 
I did take some pictures but not yet uploaded them, I'll see if I can do this tomorrow now.

Since visiting the property I have added some of my own codes as a learning exercise.

I do not do EICR's as I believe this is currently beyond my limitations as I do not have knowledge of previous edition wiring regs and unable to date installations. If anyone can add to the codes without seeing the photos it would be appreciated to see how my virtual coding does :D

I just thought I would also mention that the Landlady has already been out and purchased a 17th edition dual RCD Wylex so seems to be taking the report serious enough to realise improvements are required but she also stated that she thought the EICR carried out was way over the top and that she is not particularly happy.

Happy reading and thanks in advance for any assistance or advice offered :thumbsup

1SC


Consumer Unit is not accessible without needing a hammer and screwdriver to open wooden boxing in C2
C3

Both consumer units no danger or warning labels C3

C3

DB1 consumer unit cover missing, exposed busbar C1
I disagree. C1 = Immediate Danger I would use a C2 as the cu is contained within the boxing and only become dangerous if opening the door and sticking hand inside. Definitely unacceptable but not a C1 in my opinion.

No main Earth to Gas intake C1
No main Earth to water C1
C2 in my opinion

Washing machine is connected to a 4 way extension, extension lead then is run behind a gas cooker C2

C3

Gas cooker is on long flex C2

C3 - flex is under 2 metres in length. I would be more concerned that the flex travels up the side of the cooker and over the work top to the first available socket

Kitchen downlight clip is missing and lamp hanging from fitting C2
C3 - Lamp retaining clip not present, out of reach and no sufficient weight to warrant a code 2 (IMO)

No fan isolation in kitchen - C3

Kitchen is well lit during the daytime so can be isolated at the board for maintenance purposes - No code

No apparent Supplementary Bonding C2
Agree

No apparent Supplementary Bonding to shower room C2

Agree

Bedroom socket is broken C1
Bedroom socket back box cracked and holed C2 - you would have to stick your finger in the hole to get lucky

Bedroom socket loose?

I struggled to find this but believe it to be the same socket that is cracked and holed and would have listed it in the same observation.

Bedroom socket behind door and flex running under carpet to a 4 way extension lead C3

Now the leads are above the carpet running straight across the door lol Unplug it and no code ? :D

Joint box in bathroom exposed cable entries C1
Adaptable box not fitted with appropriate glands C2 or could it even be a code 3???

No fan isolation to shower fan C3
No windows so fan isolation required C3

Bathroom fan appears to be 230v unable to locate transformer C1
Banana split! 230v fan OUTSIDE OF ZONES! NO CODE. 2.4 metres from shower tray to fan OR 2.7 metres from floor to fan!

Shower switch is a 1 way consumer unit outside shower room (recommend 45A switch fitted) C1

My concern with this one is that the current mcb is fouling the bathroom door which could lead to damage to which could result in live parts becoming exposed but I still think it could only warrant a code 3???

Hallway socket is unswitched recommend this to be changed to switched C3

Would this really warrant a code?

Boiler has been replaced so cannot comment - Location changed also

Lights are doubled up in the consumer unit they have separate fuses - C2
unable to comment

Recommend mains smoke detectors to be fitted C3

No code - Battery smokes fitted?

No apparent fire blanket

No apparent fire extinguishers

As this property is being provided for students recommend emergency lighting is installed
Should this type of thing be recorded in an EICR? perhaps a separate advisory sheet?

Recommended upgrading main tails C3

C3
Recommended upgrading main earth from 6mm to 16mm C2
C2

No apparent switch live ident C3
C3

Downstairs sockets neutral to Neutral open circuit C1

C2 if a C1 is awarded then it needs correcting there and then or the client is to be informed in writing. If it was a C1 then why was the circuit left in use? Bizarre.
 
This may of just been my old company policy but should'nt C1's be rectified there and then by you as it is an immediate danger? ie bare live cables, missing DB cover (obviously not this one because a tool is required to access it)
 
should'nt C1's be rectified there and then by you as it is an immediate danger?

That is correct indeed, even I know that and I don't do them :)

The exposed busbar was within a boxing in section but did not require a tool although there is no reason to go in there other than if a fuse needed to be replaced but giving what I have just mentioned does it warrant a 1 as it is not directly on show?

Thanks

1SC:)
 
@ 1shortcircuit. i have just read you post#18 and , without seeing the job, i think the codes et.c you have suggested for the various faults are pretty much in agreement with what i would have said. a lot of them are quick fixes, so get on with it and earn a wage out of it. make sure you get plenty of these :coffee::coffee:
 
  • Like
Reactions: 1 person
Only read the first couple of pages, **** suitably boiled!!!!

Apparently doesn't know the difference between U & Uo, and, the world will end if you dont have an RCD!!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Review if Electrical Installation Condition Report coding used?
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
23

Advert

Thread statistics

Created
1shortcircuit,
Last reply from
Guest123,
Replies
23
Views
9,394

Advert