Hi all,
I'm still learning this stuff so go easy!
I've just carried out a ring final circuit test. Having identified both legs of the ring I began testing between both ends of the line conductor, which has given me an infinite reading on the meter. I also got the same result on the cpc. When testing the neutral I get 0.56 ohm..
The answer to me suggests I have an open cpc and neutral on the circuit. Am I on the right path here, or have I missed something?
Thanks in advance!
The tester is a Fluke 1653B
I'm still learning this stuff so go easy!
I've just carried out a ring final circuit test. Having identified both legs of the ring I began testing between both ends of the line conductor, which has given me an infinite reading on the meter. I also got the same result on the cpc. When testing the neutral I get 0.56 ohm..
The answer to me suggests I have an open cpc and neutral on the circuit. Am I on the right path here, or have I missed something?
Thanks in advance!
The tester is a Fluke 1653B