Testing a consumer unit with horizontal trunking above it. On investigation trunking has been used to extend the cables into CU. The cables are block connected in the trunking to extend them.
Testing the ring continuity, r1, end to end I discover a dead short. 2 legs leave CU to be joined in the same block connector to the 2 legs leaving the trunking for the sockets.

Testing r1 at a socket it's obviously Ok. The ring is complete it just does not start in the CU. Is this Ok?
 
Is this one of the 'lollipop' rings? aDaz
 
Heard it thrown about before, but it makes sense, have seen it done with a 6mm feeding a ring circuit. What size cables leave the CU to join the ring conductors?
 
It is indeed. Well, based on what the ring actually looks like. Daz
 
For it to be a correct ring main it must start and end in the consumer unit,
personnally i use push in connectors to extend wiring in consumer unit if needed, smaller than connection blocks/or choc block, try looking at the link to line junction boxes they have the cheapest push in connectors, also senate do them "Ideal" have now released some lovely little orange ones brill in board as take up no room cable in each end, take up to 2.5mm so most wiring.
Anyway ring must start and end at board otherwise the first bit is a radial circuit and could overload
 
For it to be a correct ring main it must start and end in the consumer unit,
personnally i use push in connectors to extend wiring in consumer unit if needed, smaller than connection blocks/or choc block, try looking at the link to line junction boxes they have the cheapest push in connectors, also senate do them "Ideal" have now released some lovely little orange ones brill in board as take up no room cable in each end, take up to 2.5mm so most wiring.
Anyway ring must start and end at board otherwise the first bit is a radial circuit and could overload

Is a lollipop ring not allowed? Even if the lead-in part is (for example) 6mm? Daz
 
The first bit can't overload anymore than a ring could. It's 2 wires (2.5) just the same as a ring.
 
fog;736373 Anyway ring must start and end at board otherwise the first bit is a radial circuit and could overload[/QUOTE said:
Surely not if appropriate sized conductors are used, it sounds like when the CU was changed they didn't extend the individual conductors and just connected them together, op did you try getting your readings from after the connector block?
 
also senate do them "Ideal" have now released some lovely little orange ones brill in board as take up no room cable in each end, take up to 2.5mm so most wiring.


"line" do them as well, yellow. cable in each end. just a little bit bulkier than a through crimp. lubbly jubbly.


 
I meant directly after the connector block, disconnect from there and took the end to ends. Sounds like what I mentioned earlier mate but could be wrong, the individual conductors should have been extended back into the CU to maintain a complete ring. But tbh if it's a 2 x 2.5mm radial for a really short run above the CU it's probably not that big a deal, as they can carry enough amps and like the others have said, giving a lollipop ring
 
"line" do them as well, yellow. cable in each end. just a little bit bulkier than a through crimp. lubbly jubbly.
Are they on their website yet, tel? I couldn't find them.
 
Can you not just pull a new leg in from the first socket of the ring and then take it to the CU?
 
I could just remove the block connector and crimp the 2 legs to the 2 wires and it's fixed. I was just wondering if it was a fault then what code would I give it on the EICR?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Ring main
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
16

Advert

Thread statistics

Created
eckersecker,
Last reply from
Brightspark2,
Replies
16
Views
2,017

Advert