Just trying to double check if there's a reg suggesting a 3phase circuit should have over-current device that disconnects all line conductors at once? Got an old rewireable board supplying 3phase motors with 3 individual fuses.

I'm looking at 530.3.1 ...................

Can anyone confirm this?

Thank!!
 
Not all three phase circuits are protected by a device that disconnects all three phases, you said in your post that you have a large rewireable D/B thats quite common in industrial installations, most final circuits (three phase motors for example) would have their own individual protection, which would sense an over current in one of the phases. should one of the main phases go open circuit 530.3.1 deals with this scenario (a contactor motor starter) as an example. Your board should supply the motors via a starter.
 
Agree as Pete999 has stated...

There are 3 phase switch fuses/fuses switches etc, that use special striker fuses, that release a short rod. So that when any of the fuses operate, the released fuse rod hits a striker plate that opens the load contacts to all 3 fuses.
 
something like this (overload heater block)m9c7i3zFbLN1JGiBc-eKBvQ.jpg
we are phasing them out in some of the older equipment in our plant
damn things are a pain to find.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Separate fuses for 3phase supply
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
James sparks,
Last reply from
gnuuser,
Replies
3
Views
1,914

Advert