Hi all
I am fitting a oven with a separate electric hob
Oven is 3400w so going to use 10m of 3mm twin and earth on a 16a mcb
Electric hob is 6500 so 10m of 6mm on a 32 amp mcb
Question is do i have to fit 2 cooker out lets and 2 dp switches or can i run both oven and hob into 1 cooker outlet and 1 dp switch
Obviously i will have to up the cable and the mcb
So 10m of 10mm twin and earth on a 50a mcb
So what does yous think
Thanks
 
Providing both units are rated between 15 and 50 amps and within 2 mtrs of switch you can use one




Chris
 
So that a yes then nice 1

so from the above
6500w/230 =28.2 so 30a
3400/230 =14.7 so so 16a
so with diversity and just to be on the safe side a 45a mcb on 10mm cable will be fine?
 
Last edited by a moderator:
Should be fine, 10mm cable can take over 60amps as long as it is not seriously derated by its installation method ie thru insulation.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Separate oven and cooker info
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
3

Thread Tags

Advert

Thread statistics

Created
simonmx23,
Last reply from
pushrod,
Replies
3
Views
2,572

Advert