Cooker circuit has B40 MCB in the CU for the cooker, confirmed wired to the cooker outlet throughout, via a cooker switch & socket with a 10mm cable.

Issue is new cooker has a 1.5mm cable (fitted by manufacturer see image). It is 3.22KW rated load, and 16A fuse rating. The cooker connection too small to fit 10mm cable to.
Hob is gas but attached plug for ignition.

How to deal with this in a safe and sensible way? thanks.IMG_7046.jpeg
 
Last edited by a moderator:
Fused spur or plug and socket?
 
  • Like
Reactions: Dustydazzler
Fused spur or plug and socket?
I did consider the fused spur from the 10mm cable, but I’m not sure we can get the 10mm into one end of a spur. It’s probably the easiest of answers with that circuit in place, but I don’t know what the professional electricians would say about that. As much as it pains me, I’m considering putting a new MCB, say 32A, in a spare slot on the CU, a 4mm cable across to similar area and find a way from there, perhaps on another’s cooker switch. I find it bazaar that a new cooker is run on effectively what looks like a thin kettle lead.
 
3.22kW by 230v is exactly 14A, well within the design of 1.5mm cable.

How is the cooker connected? To a regular cooker outlet plate that already exists? Just connect the 1.5 to the 10 there, and downgrade the circuit breaker to 16A.
You won’t need to change the wiring in any way.

If the cooker comes with a cable attached, you’re not supposed to change it…

A cooker is classed as a fixed load…. It won’t be able to pull any more than the 3.22kW stated.
 
3.22kW by 230v is exactly 14A, well within the design of 1.5mm cable.

How is the cooker connected? To a regular cooker outlet plate that already exists? Just connect the 1.5 to the 10 there, and downgrade the circuit breaker to 16A.
You won’t need to change the wiring in any way.

If the cooker comes with a cable attached, you’re not supposed to change it…

A cooker is classed as a fixed load…. It won’t be able to pull any more than the 3.22kW stated.
Yes that sounds like a good solution. But just thinking about the plug socket on the cooker switch do I need to have a higher circuit breaker to accommodate that socket?
 
Don't see a problem with the 32A MCB, as far as the 1.5mm2 cable is concerned. It's a fixed load, so overload protection is not required, and in the event of a live to earth short circuit, it's no different to a short circuit live to earth on a spur off of a ring, where the 1.5mm2 cpc carries the full fault current.
Whether the oven manufacturer requires 16A fusing for the actual appliance is a different matter.
 
3.22kW by 230v is exactly 14A, well within the design of 1.5mm cable.

How is the cooker connected? To a regular cooker outlet plate that already exists? Just connect the 1.5 to the 10 there, and downgrade the circuit breaker to 16A.
You won’t need to change the wiring in any way.

If the cooker comes with a cable attached, you’re not supposed to change it…

A cooker is classed as a fixed load…. It won’t be able to pull any more than the 3.22kW stated.
Okay guys worked perfectly on a 16A fuse until I pushed it to the limit heat wise AND plug the kettle in to test. That tripped the 16A MCB
 
2kW kettle?
That’s roughly 8A of your 16, so yes, it will trip.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Norwich
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Cooker circuit with new appliance not matching
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
Smasher,
Last reply from
littlespark,
Replies
7
Views
2,108

Advert