Electrics to shed. No water or gas.
Consumer unit in the middle of the house at the bottom of a nicely decorated wall with concrete floors.
In other words, no chance of separate circuit.
All earthing present and correct.

Rcd covering kitchen circuit and others.


Thinking of connecting to said 4mm kitchen radial on a 32 amp breaker Zs .32 at this point(Double socket)
Run another 4m in 4mm t&e(under units) to outside wall.
Connect to 6mm 3 core swa for 30 m (down and under garden) to brick shed to supply a 20 amp radial and 6 amp lighting circuit. metal consumer unit.
Any thoughts greatly appreciated.

Dave G
 
Can you not exit through the rear of the CU or just below or above and form a new circuit? or is the CU full to capacity? it's just a thought, you could then exit the CU in PVC/PVC and joint to the SWA in an adaptable box, not being able to see the set up. it's only a suggestion.
 
Why the 6mm armoured and not 4mm?

No mention of any measurements so could he be concerned with volt drop, but like you said why 6 and not 4
 
In an ideal world it would be a new circuit but sometimes you've got to just work with what you've got. You would want some kind of double pole isolation in the house as in the event of a fault you would want to be able to isolate the outside part of the circuit so as not to affect the kitchen/other circuits on the same RCD. What's the design current of the brick shed? For example is it one light, one double socket or multiple sockets that are going to run heaters, tools, etc. How long is the existing 4mm² kitchen radial to base volt drop calculations on?
 
  • Like
Reactions: 2 people
  • Like
Reactions: 1 person
Yes 6 mm as i wanted to minimize volt drop, but also wanted a zs at shed that was low. As the point of connection to the kitchen
circuit there is already .32 impedance.
The kitchen circuit is protected with an Rcd which covers others so if in future there is a prob with the circuit tripping others i
can put it in its own CU. Its the cable i have no chance of running.
Only computers in shed with lighting no heavy heaters etc
 
As Leesparky said, I'd definitely put a double pole isolator with easy access as near to your supply connection as poss. :)
 
If the supply is to be taken from an existing circuit I would not bother with the garage CU I don't think. Just fuse down for the lights from the extended circuit.
 
Yes 6 mm as i wanted to minimize volt drop, but also wanted a zs at shed that was low. As the point of connection to the kitchen
circuit there is already .32 impedance.
The kitchen circuit is protected with an Rcd which covers others so if in future there is a prob with the circuit tripping others i
can put it in its own CU. Its the cable i have no chance of running.
Only computers in shed with lighting no heavy heaters etc


With a Zs at the point of connection of .32 using 4mm² 3core swa on a 32A type B mcb using the 3rd core as a CPC would roughly give you a maximum length of around 69 meters from the point of connection. Probably wouldn't comply for volt drop though.
 
aas previous posts, fit a 13A SFCU next to socket, then cable to shed direct to sockets, then FCU @ 5A down for loghts.
 
  • Like
Reactions: 1 person
Sheds electric
This site is full of eccentrics
Sheds done things I never expected
And I need more time
Sheds got dodge wiring
And god only knows i'll fix this
On the Consumer Unit is a burn mark
And I need more time

And I want you to know
I've got it all nearly fixed now
But I need more time
And I want you to say
Do you know what I'm saying?
But I need more ....
Coz Blue goes there and Brown here.
There's lots and lots for us to see
There's lots and lots for us to do
Shed is electric, can I be electric too?

Sheds got a consumer unit
We don't get on with one another
But I quite fancy putting an outdoor socket
And I think maybe outdoor light too
Sheds got a lighting
In fact sheds got 'bout a dozen
Shed got one in the outhouse
But it's nothing to do with me

And I want you to know
I've got it all nearly fixed now
But I need more time
And I want you to say
Do you know what I'm saying?
But I need more ....
Coz Blue goes there and Brown here.
There's lots and lots for us to see
There's lots and lots for us to do
Shed is electric, can I be electric too?

<strong style="font-size: small;"><font color="#000000"><span style="font-family: 'comic sans ms';">[video=youtube;3dUV4VAr9lk]https://www.youtube.com/watch?v=3dUV4VAr9lk[/video]
 
Last edited by a moderator:
  • Like
Reactions: 2 people

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Shed Electrics
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
optician,
Last reply from
DuaneMHunt1976,
Replies
15
Views
2,620

Advert