Have followed this forum for a long time and used it to gain confidence in getting PV system which was fitted in Sept 2011.I have a SMA 4000TL with 16 sharp 250 panels
Over the past couple of weeks have noticed that when broken cloud/sunny conditions my OWL monitor will drop to 0 for 3 minutes when sun bright and then start producing again but if power ramps up quickly it will go back to 0.
Have checked that sunny explorer shows the same so not the monitor at fault.
Grid voltage shows as 245 - 249 volts and no error messages. When no cloud ,system produces well , max of 24.4KWh one day.
Does not seem to be having a great effect on daily figures at the moment but I am curious as I would think that MPP tracker should act fast enough to control output.
 
We had a similar issue with a 4000TL. Is the inverter set to G83? Page 44 of the installation guide explains what is required. Sometimes the inverters are delivered with no country settings specified so you have to do this manually.
 
Shutdown and restarted inverter which showed AD0 for country setting instead of G83 , so will contact installer.
 
It is probably saying ADJ rather than AD0, but your installer should be able to adjust it with a grid guard code
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
SMA 4000TL unstable
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
3

Thread Tags

Tags Tags
None

Advert

Thread statistics

Created
simbob,
Last reply from
BruceB,
Replies
3
Views
2,621

Advert